    FEC's to Drive Fast Acting Actuators

    With all the dampening built into CCT, has anyone had any luck driving 3-5 second fast acting actuators with FECs? Thinking about a VAV box application as an option opposed to a venturi. I'm just worried that the delay in processing time will cause the actuator to slam open and closed and as it chases the pressure.

  2. #2
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    546
    Post Likes
    I tried one time, the results were not good. Like you said it just slammed open. Fortunately for me, it really didn't matter the damper just went full open. It was for makeup air into a lab space.

  3. #3
    Join Date
    Dec 2012
    Posts
    74
    Post Likes
    Try adjusting the time constant in the attributes for the inputs. I had to do that once since the delays were causing havoc. These selftuning PIDs aren't really ideal for dynamic systems. Derivative usually gets more emphasis for rapidly modulating controlled variables.

  4. #4
    Join Date
    Jul 2009
    Location
    Westside
    Posts
    2,083
    Post Likes
    I took a PCG/PCT class awhile back, and the loop tuning portion. Started with 60 to 70% of the time the adaptive tuning doesn't work. My next thought was ,why would I use that?? I turn off the adaptive tuning, and self tune all the pids. I've had good success doing that. In your case, I think that would be the only chance, and its still going to be tough!!

  5. #5
    Join Date
    Jan 2012
    Location
    California
    Posts
    91
    Post Likes
    Venturi valves are obviously better control because of the way the valve opens a closes. A vav box is hard to control because of the damper. If you can tune the PID and the box is sized correctly you will be able to do it but it is a real pain. We did a small hood and room pressure for one customer using VAV's and VFD's on room and hood exhaust and because of our programming capabilities we are able to do relatively good control. It is in no way the same as the Phoenix or TSI stuff we have done and do, but it met the budget needs of the customer and is reliable.

  6. #6
    Join Date
    Apr 2013
    Location
    Madison, WI
    Posts
    22
    Post Likes
    We have mastered the "art" of using FECs for fast ascitng actuators.

  7. #7
    Join Date
    Feb 2009
    Location
    Northeast
    Posts
    587
    Post Likes
    On the last 2 JCI NAE jobs that I have followed the branch into, the JCI techs had set a "Tuning Reset" schedule into the NAE to rest the tuning on a Daily or a Weekly basis. I guess the branch has trouble making it work too.

    On 1 of those sites I had to turn off the tuning on classroom unit ventilators because, over time, the tuning would get too sluggish and let the room heat a couple of degrees above setpoint for an hour or two in the morning, then come back down to setpoint in the afternoon. Of course the "problem" was the units were "cold" in the afternoon (at setpoint). Manual tuning keeps the room +-0.5°F of setpoint most of the time and complaints seemed to go away. Funny how no one ever tells you it is working better when you make these kind of adjustments.

  8. #8
    Join Date
    Apr 2013
    Location
    Madison, WI
    Posts
    22
    Post Likes

    Auto Tuning

    Auto tuning cause more issues than it prevents. I will rarely use auto tuning to try to find better numbers but the longer I use CCT the more I have figured out what numbers work well and I no longer use auto tuning. Especially with the known issue fo the PID tuning the prop band down to 0 and going unreliable. Before going unrelaible it operates as binary controller toggling between 0 and 100.

  9. #9
    Join Date
    Jan 2012
    Location
    California
    Posts
    91
    Post Likes
    Quote Originally Posted by Jmartin10 View Post
    Auto tuning cause more issues than it prevents. I will rarely use auto tuning to try to find better numbers but the longer I use CCT the more I have figured out what numbers work well and I no longer use auto tuning. Especially with the known issue fo the PID tuning the prop band down to 0 and going unreliable. Before going unrelaible it operates as binary controller toggling between 0 and 100.
    I completely agree, Auto tuning will kill you slowly or fast either way use it to find reasonable numbers then turn it off! Our optimum start will get (learn) some pretty good heat-up & cool-down numbers to start with. But over time because of auto calculating you can miss a mechanical issue creeping up onto the unit. It just keeps starting earlier and earlier as the capacity of the equipment degrades for whatever reason and you wont catch it until its a big issue.

  10. #10
    Join Date
    Apr 2013
    Location
    Minneapolis, MN
    Posts
    30
    Post Likes
    Thread Starter
    Thanks folks!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •