    chargeing with 404a

    is it ok to charge walk in freezer to full sight glass . no receiver water cooled condenser

  2. #2
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,148
    Should have a receiver if you have a tx valve.

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,587
    Quote Originally Posted by Dchappa21 View Post
    Should have a receiver if you have a tx valve.
    Not if it's not a pumpdown. Might just be using a t-stat to control compressor. A clear glass would be a starting point. SC & SH would be the proper way to go. Make sure the water regulating valve is set properly.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  4. #4
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    cycles on liquid line solinoid valve.compressor took a poop, was called to change out. copeland copelematic m. nrdi 031a tcf 800. going to change oil to ester before install. as well as ll drier and contactor. noticed someone has added suction drier canister with one core.no idea on history,not to familiar with low temp systems. thats why im asking about the charge.thanks

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,164
    No receiver ??

    Is this condenser indoor on top of freezer ?

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,587
    You've got a receiver. Check under the condensing unit
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  7. #7
    Join Date
    Oct 2012
    Posts
    10
    Yeaa full sight glass is a good start but then after you notice the bubbles just starting to disappear, start doing SH and SC. You don't want to over charge..

  8. #8
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    794
    Yeah, I bet there is a receiver under the unit.

  9. #9
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    I bet the condenser is also the receiver.

  10. #10
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    looks like discharge line off compressor goes to vessel under compressor then liquid line exits vessel to drier and sight glass then to evap to freezer. vessel has water line going into it with water regulater. regulator has cap tube that senses pressure via discharge port, then another line exiting vessel dumping water to open sight drain. dont see any receiver.

  11. #11
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    have picture on iphone not sure how to post sorry

  12. #12
    Join Date
    Jan 2010
    Location
    Vancouver Island
    Posts
    342
    Quote Originally Posted by cannedheat View Post
    looks like discharge line off compressor goes to vessel under compressor then liquid line exits vessel to drier and sight glass then to evap to freezer. vessel has water line going into it with water regulater. regulator has cap tube that senses pressure via discharge port, then another line exiting vessel dumping water to open sight drain. dont see any receiver.
    Someone correct me if I am wrong, but I believe based on the description this is a shell and coil type water cooled condenser and that the shell doubles as a receiver in this setup?

  13. #13
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    so the reciever is the vessel and the condenser water is basicly a coil in the vessel condensing hot gas into liquid and storage before entering liquid line and so on..

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event