Thread: CCN AX

  1. #14
    Join Date
    Apr 2007
    Location
    Southwest Riverside County CA
    Posts
    38
    I have a customer with CCN and multiple bldgs connected to the 0 network. They have issues with the underground between buildings and my thought was using serial RS485/ethernet converters with the first connected to the JACE with the CCN driver over the RS485 connection and the others located on each bridge using a block of static ip addresses segregated as much as possible through the net mask. Has anybody done this before? Too bad the CCN driver does not have an option for UDP so the JACE connection COM2 connection can go away and save a device.
    Also any issues with the tunnel feature?
    Thanks in advance..

  2. #15
    Join Date
    Jul 2006
    Location
    Southern California
    Posts
    223
    Most of the "EIA485 to TCP/IP converters" that I have worked with, have to be configured to wrap the UDP Packets into IP packets (similar to the BACnet BBMD Function).

    Not shure if this is anything helpful, but some EIA485 data packets need the extra coaxing to
    get thru IP switches.

    UDP are broadcasts and not forwarded thru IP switches, IP packets do make it thru IP switches.

    Maybe something to look at.

    Just some 2 bits of thoughts.

    Good luck

    Drac
    "We are what we repeatedly do. Excellence, then, is not an act, but a habit" Aristotle

    Remember to "Pay it Forward"; help out the newer generation of techs, remember someone during our career helped us! ("Pay it Forward" was by someone smarter than me!!)

  3. #16
    Join Date
    Jun 2007
    Posts
    148
    Not the best answer here, but you could use 2 carrier etherlinks and pass over their network... Just food for thought.

  4. #17
    Join Date
    Apr 2007
    Location
    Southwest Riverside County CA
    Posts
    38
    Thanks for the response. The serial device I'm looking at also does TCP/IP (B&B-elec VESR901) also so I'm going to have to play with it.
    Evidently the CCN workstation has to be setup for a connection to a carrier etherlink module using the JACE IP address when the tunneling feature is enabled.
    Thanks

  5. #18
    Join Date
    Dec 2006
    Location
    Boston area
    Posts
    212
    The Jace I was using was a demo from our Honeywell dealer

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event