    when you activate the fire supression system, should the exhaust fan stays running? (this new thread is great)

  2. #2
    Join Date
    May 2000
    Posts
    342
    Post Likes
    Fan power should be fed through a relay on the Ansel system to shut down the fans and make up air in case of fire suppression discharge.

    You will certainly find fans that do not and may be grandfathered in before a code change or were not inspected. New hood installations must be permitted just like AC systems in my state. You will be turned down if there is no integrated relay.

    I don't have a link to the code section to give you but it may vary from state to state.




  3. #3
    Join Date
    Sep 2006
    Location
    Winter Springs, Fl
    Posts
    1,756
    Post Likes
    As far as I know in Fla, all power is required to be removed from the hood except the exhaust fan ( i.e. lights, makeup fan, any receptacles under the hood ) during an Ansel trip. It has to be controlled through a relay panel. IMO.

  4. #4
    Join Date
    Jan 2003
    Location
    San Jose, Ca
    Posts
    2,089
    Post Likes
    Fans should shut down.
    Old snipes don't die they just loose their steam

  5. #5
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,117
    Post Likes
    In NJ exhaust fan stays on to remove smoke and MUA fan turns off with supression system activation.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  6. #6
    Join Date
    May 2002
    Location
    springdale arkansas
    Posts
    15
    Post Likes
    in arkansas vents stay on electric gas and mau all shut off