I'm not sure about that unit in particular, but some units must have a G call with W for the furnace to come on.
i have a 48tme012 and the only way that I get the heating call to work is to turn the IDF to on,then eveything will run IDF and burners come on and will cycle on the therm for temp. If fan left in auto the unit will not do anything. I disconected the therm wires at unit and jumped out r-w1 no action but r-w1 and g unit starts. The ignitor module and limin switch were replaced July,2012
I'm not sure about that unit in particular, but some units must have a G call with W for the furnace to come on.
What are the first five digits of the serial number?
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
is there a time delay relay in the unit?
The unit should start in heat mode with a closure for R to W1. We're there any alarm codes blinking on the igc? Is there a basic stat on it or any other controls?
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
I'm curious as to why the igc board and limit were replaced in July. Were they causing issues in a/c mode?
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
Once the igc goes into lockout the inducer stays on even after the limit becomes closed. This would have been indicated by the flashing red light. Next question. You said you disconnected the t-stat and then jumped out. Was this done at the unit or inside by the thermostat?
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
48tme012-a-501
On the icb, when you installed it did you reverse the L1 blower tap with the L1 combustion tap?
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING