Results 1 to 10 of 10
    I have a Rheem furnace with 5 inshot burners in it. Sometimes only the burner on the far right comes on and after about 5 seconds the unit shuts down then the fan only runs. I have checked and cleaned the crossovers and aligned the burners and checked the gas pressures into valve 12"wc and out is 11"wc. can anyone help me, this is frustrating>
    chicago suburbs
    12" wc?
    FILL OUT YOUR PROFILE!!
    Rheem furnace problem
    12"wc is 12 inches of water colume gas pressure on LPG
    Memphis
    did u check the orfices to make sure a spider web didnt clog up the 2nd one?
    Life is like a jar of jalapenos. What you do today might burn your ass tomorrow.
    How many volts do you have at the gas valve?
    Philadelphia, PA
    Shut the furnace of and call an experienced service tech to test and diagnose the system. This can be very dangerous especially with LPG.
    Apr 2004
    Why did you set it up for 11"? (I realize it's LP) Did you read that in a manual somewhere? 'Cause it isnt anywhere in the manual for your furnace.
    CHECK ORFICES AT BEGINNG OF BURNERS TAKE THEM OUT AND CHECK FOR SPIDER WEBS INSIDE
    Frown
    Manual says 12-14 inches water colum.
    Apr 2004
    inlet maybe, not outlet.