Thanks for the additional info. I thought that might be where the equipment would be located.
I would have suggested zoning the first floor system to handle the basement area. Anyway, it's to late now so let's fix what you have.
I'm assuming the 6" return is in the mechanical room? If so, make it a 12" to a (new) larger grille.
I hope this helps you.
-
11-10-2012, 07:15 PM #15
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819
If it's easier for you to carry on this conversation without visiting this site, my email address is in my bio. Just an FYI.
-
11-10-2012, 08:09 PM #16
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
Your welcome! The tech that came even said that for heating and cooling basements he recommends zoning from the first floor system.
Are you talking about the 6 inch return going into the man cave? If you are then yes, the 6 inch return is coming from the mechanical room. Upsizing the return could be a lot easier than adding a new one.
-
11-10-2012, 08:14 PM #17
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
-
11-10-2012, 08:46 PM #18
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
-
11-10-2012, 10:58 PM #19
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819
Thanks for the picture. They are helpful. The 12" is connected to a filter grille and the 6" is not a filter grille. How many filters are in the system?
Also, what size is that filter grille? If it's a 16"x25" (800cfm), then (if possible) a larger pipe could go there for more RA.
Honestly, I don't know why anyone would run just one 6" supply to any basement room other than a small bathroom.
-
11-10-2012, 11:12 PM #20
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
Your welcome. There used to be a filter in the 12 return filter grille but then the 6 inch return was added to the man cave which made us put a 14 x 20 filter in the air handler. The filter grille is a 14" x14". I just measured it.
I agree, 6 inch sounds too small for basement rooms.
-
11-10-2012, 11:22 PM #21
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819
You're up late!
The 14"x20" is only good for 580cfm. This is even less than the 12" flex pipe that serves it!
The 6" pipe is about 100cfm.
I imagine the electric heat needs at least 1,000cfms to perform well. I'm not to fimiliar with electric heat as far as a limit (switch) is concerned.
-
11-10-2012, 11:26 PM #22
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
It's only 11:26 PM Eastern right now!
That's still kinda late though.
Oh 14" x20"? My mistake. The airflow does feel weak going into the 6 inch return. I can feel a lot of air getting sucked in through the 12 inch.
When the tech was here he did replace the contactor in the air handler because the old one was burnt up.
-
11-10-2012, 11:49 PM #23
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819
You said 14"x20" is a mistake? Is the size different? Ya, 6" doesn't do much, plus that grille appears on the small side as well.
A limit switch on a gas furnace turns off the gas (burners) if there is not enough airflow.
I'm sure an electric furnace has something like that.
I know ur an hour ahead of us here in the midwest. I'm watching the Oregon/Cal game.
-
11-10-2012, 11:51 PM #24
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
-
11-10-2012, 11:54 PM #25
Regular Guest
- Join Date
- Sep 2012
- Location
- North GA
- Posts
- 321
-
11-11-2012, 12:12 AM #26
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,819


Reply With Quote