Results 1 to 3 of 3
  1. #1
    Join Date
    Dec 2003
    Location
    Salisbury, MD.
    Posts
    1,499
    Post Likes

    trane ah and climatemaster cond unit

    I have a Trane mod. TAM7AOC60H51SBA air handler and a climatemaster mod. TTS049AGC00NNNS cond. unit.with a Honeywell T8320U thermostat. I have a couple of questions.
    1. What do the G and W terminals do on the condensing unit?
    2. Does any one have a wiring diagram for the pair?
    3. How should I wire a Honeywell tru-steam into the system.
    I have never used or worked on this air handler before so I am unfamiliar with it's operation.
    I am using an open loop and on second stage heat the air handler is obnoxiously loud and the system seems to short cycle. The system is sized properly as this unit replaced a FHP 048 self contained unit. I located the cond. unit under the house in hopes it would be quieter. I don't hear the cond. unit, but the airflow is loud. I have gone through and adjusted the dip switches per the manual. I have a very short return which does account for some of the noise which I do plan on repairing at a later date.

  2. #2
    Join Date
    Dec 2003
    Location
    Salisbury, MD.
    Posts
    1,499
    Post Likes
    Thread Starter
    any ideas?

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,136
    Post Likes
    Quote Originally Posted by freonjohn View Post
    I have a Trane mod. TAM7AOC60H51SBA air handler and a climatemaster mod. TTS049AGC00NNNS cond. unit.with a Honeywell T8320U thermostat. I have a couple of questions.

    1. What do the G and W terminals do on the condensing unit?

    If I read it correctly, they are used to activate Emergency Heat while the TTS unit is in Lockout Mode.

    2. Does any one have a wiring diagram for the pair?

    Check your email.

    3. How should I wire a Honeywell tru-steam into the system.

    I've never installed one of these, but doesn't the True Steam Installation Manual explain this?
    *
    Instead of learning the tricks of the trade, learn the trade.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.