chargeing with 404a
is it ok to charge walk in freezer to full sight glass . no receiver water cooled condenser
-
11-09-2012, 07:32 PM #2
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 916
Should have a receiver if you have a tx valve.
-
11-09-2012, 07:39 PM #3Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-09-2012, 08:01 PM #4
Regular Guest
- Join Date
- Feb 2006
- Location
- indiana
- Posts
- 75
cycles on liquid line solinoid valve.compressor took a poop, was called to change out. copeland copelematic m. nrdi 031a tcf 800. going to change oil to ester before install. as well as ll drier and contactor. noticed someone has added suction drier canister with one core.no idea on history,not to familiar with low temp systems. thats why im asking about the charge.thanks
-
11-09-2012, 08:06 PM #5
No receiver ??
Is this condenser indoor on top of freezer ?
-
11-09-2012, 08:20 PM #6
You've got a receiver. Check under the condensing unit
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-09-2012, 08:24 PM #7
Regular Guest
- Join Date
- Oct 2012
- Posts
- 10
Yeaa full sight glass is a good start but then after you notice the bubbles just starting to disappear, start doing SH and SC. You don't want to over charge..
-
11-09-2012, 08:45 PM #8
Professional Member*
- Join Date
- Oct 2009
- Location
- Raleigh, NC
- Posts
- 435
Yeah, I bet there is a receiver under the unit.
-
11-09-2012, 09:16 PM #9
I bet the condenser is also the receiver.
-
11-09-2012, 11:31 PM #10
Regular Guest
- Join Date
- Feb 2006
- Location
- indiana
- Posts
- 75
looks like discharge line off compressor goes to vessel under compressor then liquid line exits vessel to drier and sight glass then to evap to freezer. vessel has water line going into it with water regulater. regulator has cap tube that senses pressure via discharge port, then another line exiting vessel dumping water to open sight drain. dont see any receiver.
-
11-09-2012, 11:55 PM #11
Regular Guest
- Join Date
- Feb 2006
- Location
- indiana
- Posts
- 75
have picture on iphone not sure how to post sorry
-
11-10-2012, 12:28 AM #12
Professional Member
- Join Date
- Jan 2010
- Location
- Vancouver Island
- Posts
- 90
-
11-10-2012, 01:09 AM #13
Regular Guest
- Join Date
- Feb 2006
- Location
- indiana
- Posts
- 75
so the reciever is the vessel and the condenser water is basicly a coil in the vessel condensing hot gas into liquid and storage before entering liquid line and so on..