    Appion TEZ 8 pump and oil.

    Went to use mine for the 3rd/4th time today after changing the oil and had issues pumping past 2000 microns. Switched to a 6CFM pump and had no issues.

    Now that I'm thinking about it I didn't use Appion oil but standard vacuum pump oil that I use in every other pump. Anyone do this with negative effects? At time I was thinking it wouldn't make a difference but now I'm regretting my choice.



    Any other feedback on this pump?

  2. #2
    Join Date
    May 2011
    Location
    Oklahoma
    Posts
    362
    I think people have used non-appion oil before with good success. Did you change anything when you swapped pumps at all?

  3. #3
    Join Date
    Jun 2008
    Location
    Baltimore, MD
    Posts
    15
    Nothing at all. Noticed it was taking an unusual amount of time for the system to pull down so I valved off the system and tried to pull only the gauges and micron gauge down. Would not pull under 700-800 microns. Switched pump and that one pulled the gauges down to 200 ish, full system to 400 in about 10min or so.