    when charging a walk in freezer, is it ok to charge to a full sight glass. there isnt a receiver. 404a.
    Sep 2006
    Ohio
    If the SC looks good and the glass is still flashing, stop charging. You are more concerned with the SC than the sight glass.
    Nov 2011
    North sweden, Umeε, Where the birches growing without limits.
    I've been told by my more learned colleauges that a system with txv and no reciever is pretty sensitive to charge. If it's not in right temp area. Charge'til it almost no flash. When close in themp it will stop flash and become clean sight glass. This is what i've performed on a pair of coolmax freezer units w/no reciever. Success every time. Ah... Subcool... let it be 'bout 5-6degF
    I dont use site glass for anything!
    Maryland
    No receiver, that could be a problem when it satisfies and pumps down. It does pump down, right?
    Quote Originally Posted by bigger b View Post
    That would depend on a number of factors.
    Length of the liquid line being pumped down would be the biggest.
    Jul 2012
    Western KY
    Walk in freezer with no receiver? Flashing sight glass is OK? Umm no!! TXV must have full colum of liquid. You cannot adjust TXV to proper superheat with out a full colum of liquid feeding it. It will hunt and never stabilize. Are you sure there is not a receiver?
    Dec 2012
    reason number 1 why manufacturers are getting rifd of sight glasses, people rely on them. weed out the non-professionals
    Dec 2012
    at least thats what all of the trade-show guys keep preaching to us and it seems to make sense.
    Mar 2009
    Mid-Mo
    Quote Originally Posted by rmitch78 View Post
    I disagree with that statement. So if you mis-interpret your meter, you should not use it anymore? Sight glasses have their place and their purpose and refrigeration work is where you'll see them the most.
    Very bold statement to be making.
    Got proof?
    Dec 2012
    well, companies that use sporlan and danfoss told us that's why manufacturers are *trying* to do away with them on their systems. maybe not weed out the suckers like i mis-spoke, but to try to differ people from relying on them i should have said.
    Dec 2012
    to quote national: "Do not replenish refrigerant solely because of bubbles in the sight glass. First find out the cause of the bubbles!" I'm thinking fractionization has an additional effect.