charging 404a system
when charging a walk in freezer, is it ok to charge to a full sight glass. there isnt a receiver. 404a.
-
11-10-2012, 09:23 AM #2
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 347
If the SC looks good and the glass is still flashing, stop charging. You are more concerned with the SC than the sight glass.
-
11-14-2012, 04:05 PM #3
Regular Guest
- Join Date
- Nov 2011
- Location
- North sweden
- Posts
- 41
I've been told by my more learned colleauges that a system with txv and no reciever is pretty sensitive to charge. If it's not in right temp area. Charge'til it almost no flash. When close in themp it will stop flash and become clean sight glass. This is what i've performed on a pair of coolmax freezer units w/no reciever. Success every time. Ah... Subcool... let it be 'bout 5-6degF
-
11-14-2012, 10:17 PM #4
I dont use site glass for anything!
-
11-14-2012, 10:31 PM #5
Regular Guest
- Join Date
- Oct 2004
- Location
- Maryland
- Posts
- 45
No receiver, that could be a problem when it satisfies and pumps down. It does pump down, right?
-
11-15-2012, 06:18 AM #6
-
11-15-2012, 09:30 AM #7
Walk in freezer with no receiver? Flashing sight glass is OK? Umm no!! TXV must have full colum of liquid. You cannot adjust TXV to proper superheat with out a full colum of liquid feeding it. It will hunt and never stabilize. Are you sure there is not a receiver?
-
12-03-2012, 08:34 PM #8
Regular Guest
- Join Date
- Dec 2012
- Posts
- 6
reason number 1 why manufacturers are getting rifd of sight glasses, people rely on them. weed out the non-professionals
-
12-03-2012, 08:36 PM #9
Regular Guest
- Join Date
- Dec 2012
- Posts
- 6
at least thats what all of the trade-show guys keep preaching to us and it seems to make sense.
-
12-03-2012, 08:42 PM #10
-
12-03-2012, 09:16 PM #11
-
12-03-2012, 10:46 PM #12
Regular Guest
- Join Date
- Dec 2012
- Posts
- 6
well, companies that use sporlan and danfoss told us that's why manufacturers are *trying* to do away with them on their systems. maybe not weed out the suckers like i mis-spoke, but to try to differ people from relying on them i should have said.
-
12-03-2012, 11:25 PM #13
Regular Guest
- Join Date
- Dec 2012
- Posts
- 6
to quote national: "Do not replenish refrigerant solely because of bubbles in the sight glass. First find out the cause of the bubbles!" I'm thinking fractionization has an additional effect.