I had spoken to a contractor who sounded like he was actually giving me good advice and knowledge, and after reading some more after the conversation, I've decided to go with a media filter instead of eac. in regards to this, just a quick question regarding some of the concerns ive read about,
i have a somewhat entry level furnace, single stage 75k btu, blower rated at around 1100~cfm. the aprilaire merv 11 media is rated at 0.08 wc drop. will i have an issue with pressure?
-
11-09-2012, 02:18 PM #2
What size is the filter?
As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84
-
11-09-2012, 02:19 PM #3
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
It'll depend on the RA ductwork and grilles. Note: Normally the supply side is okay.
-
11-09-2012, 02:22 PM #4
Regular Guest
- Join Date
- Nov 2012
- Posts
- 8
oh sorry, thought i had typed that out
. the aprilaire 2210 / 210 filter
-
11-09-2012, 02:26 PM #5
Regular Guest
- Join Date
- Nov 2012
- Posts
- 8
duct is 16x25 (filter size) picture
-
11-09-2012, 02:35 PM #6
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
The drop (pictured) is fine. I'm asking about the ductwork size above it. Which way does the ductwork go? Is it a pretty even split? How many returns are off each end? How many RA grilles are there in the home?
The ductwork/grilles will be the problem, if any, not the AprilAire 2200. You said 2210? Is that a smaller one?
-
11-09-2012, 02:40 PM #7
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
11-09-2012, 02:46 PM #8
Regular Guest
- Join Date
- Nov 2012
- Posts
- 8
-
11-09-2012, 02:48 PM #9
Regular Guest
- Join Date
- Nov 2012
- Posts
- 8
-
11-09-2012, 03:06 PM #10
It's rated at; Air Flow @300 Fpm with Initial Resistance @0.08 in WC, Final Resistance @0.5 In WC.
The filter's free-air-area will put the initial velocity around twice that 300-fpm number.
A 16X25 filter is 400-sq,ins / 144 is 2.77-sf; * using .65% free-air-area = 1.8-sf.
1100-CFM / 1.8-sf is 611-fpm velocity through a new clean filter.
A pleated filter is usually rated at 500-fpm initial velocity; therefore, the pressure drop will be considerable greater than what is stated at 300-fpm.AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
11-09-2012, 04:11 PM #11
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
Udarrell....I don't think the picture he sent was the AprilAire 2210. I'm assuming that the new filter will be much thicker.
The 2 returns don't sound like enough. what size are the grilles and where are they located? Floor or wall?
I have never heard of the 2210...I'll go online and have a look.
-
11-09-2012, 04:22 PM #12
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
I went to the AprilAire website and the model 2210 (media) looks very much like a Bryant/Carrier "E-Z flex" media.
The site said the maintenance requirerment is 1 to 2 years..............Right!
-
11-09-2012, 04:53 PM #13
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251


Reply With Quote