Results 1 to 13 of 17
    Nov 2012
    Media filter pressure question
    I had spoken to a contractor who sounded like he was actually giving me good advice and knowledge, and after reading some more after the conversation, I've decided to go with a media filter instead of eac. in regards to this, just a quick question regarding some of the concerns ive read about,
    i have a somewhat entry level furnace, single stage 75k btu, blower rated at around 1100~cfm. the aprilaire merv 11 media is rated at 0.08 wc drop. will i have an issue with pressure?
    Jun 2007
    What size is the filter?
    Dec 2010
    It'll depend on the RA ductwork and grilles. Note: Normally the supply side is okay.
    Nov 2012
    oh sorry, thought i had typed that out . the aprilaire 2210 / 210 filter
    Nov 2012
    Quote Originally Posted by George2 View Post
    duct is 16x25 (filter size) picture
    Dec 2010
    The drop (pictured) is fine. I'm asking about the ductwork size above it. Which way does the ductwork go? Is it a pretty even split? How many returns are off each end? How many RA grilles are there in the home?
    The ductwork/grilles will be the problem, if any, not the AprilAire 2200. You said 2210? Is that a smaller one?
    Quote Originally Posted by a176 View Post
    Where are you getting the 0.08 pressure drop from?
    Nov 2012
    spec sheet
    Nov 2012
    its a pretty even split yes. i have two returns, one coming from 1st floor, other coming from second floor. 2210 is the current model, its 25" depth.
    Jun 2005
    SW Wisconsin
    i have a somewhat entry level furnace, single stage 75k btu, blower rated at around 1100~cfm. The aprilaire merv 11 media is rated at 0.08 IWC drop. will I have an issue with pressure?
    It's rated at; Air Flow @300 Fpm with Initial Resistance @0.08 in WC, Final Resistance @0.5 In WC.
    The filter's free-air-area will put the initial velocity around twice that 300-fpm number.
    A 16X25 filter is 400-sq,ins / 144 is 2.77-sf; * using .65% free-air-area = 1.8-sf.
    1100-CFM / 1.8-sf is 611-fpm velocity through a new clean filter.
    A pleated filter is usually rated at 500-fpm initial velocity; therefore, the pressure drop will be considerable greater than what is stated at 300-fpm.
    Dec 2010
    Udarrell....I don't think the picture he sent was the AprilAire 2210. I'm assuming that the new filter will be much thicker.
    The 2 returns don't sound like enough. what size are the grilles and where are they located? Floor or wall?
    I have never heard of the 2210...I'll go online and have a look.
    Dec 2010
    I went to the AprilAire website and the model 2210 (media) looks very much like a Bryant/Carrier "E-Z flex" media.
    The site said the maintenance requirerment is 1 to 2 years..............Right!
    On a very clean house with no activity.