    I had spoken to a contractor who sounded like he was actually giving me good advice and knowledge, and after reading some more after the conversation, I've decided to go with a media filter instead of eac. in regards to this, just a quick question regarding some of the concerns ive read about,

    i have a somewhat entry level furnace, single stage 75k btu, blower rated at around 1100~cfm. the aprilaire merv 11 media is rated at 0.08 wc drop. will i have an issue with pressure?

  2. #2
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420
    Post Likes
    What size is the filter?
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  3. #3
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,744
    Post Likes
    It'll depend on the RA ductwork and grilles. Note: Normally the supply side is okay.

  4. #4
    Join Date
    Nov 2012
    Posts
    8
    Post Likes
    Thread Starter
    oh sorry, thought i had typed that out . the aprilaire 2210 / 210 filter

  5. #5
    Join Date
    Nov 2012
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by George2 View Post
    It'll depend on the RA ductwork and grilles. Note: Normally the supply side is okay.
    duct is 16x25 (filter size) picture

  6. #6
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,744
    Post Likes
    The drop (pictured) is fine. I'm asking about the ductwork size above it. Which way does the ductwork go? Is it a pretty even split? How many returns are off each end? How many RA grilles are there in the home?

    The ductwork/grilles will be the problem, if any, not the AprilAire 2200. You said 2210? Is that a smaller one?

  7. #7
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,095
    Post Likes
    Quote Originally Posted by a176 View Post
    I had spoken to a contractor who sounded like he was actually giving me good advice and knowledge, and after reading some more after the conversation, I've decided to go with a media filter instead of eac. in regards to this, just a quick question regarding some of the concerns ive read about,

    i have a somewhat entry level furnace, single stage 75k btu, blower rated at around 1100~cfm. the aprilaire merv 11 media is rated at 0.08 wc drop. will i have an issue with pressure?
    Where are you getting the 0.08 pressure drop from?

  8. #8
    Join Date
    Nov 2012
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by second opinion View Post
    Where are you getting the 0.08 pressure drop from?
    spec sheet

  9. #9
    Join Date
    Nov 2012
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by George2 View Post
    The drop (pictured) is fine. I'm asking about the ductwork size above it. Which way does the ductwork go? Is it a pretty even split? How many returns are off each end? How many RA grilles are there in the home?

    The ductwork/grilles will be the problem, if any, not the AprilAire 2200. You said 2210? Is that a smaller one?
    its a pretty even split yes. i have two returns, one coming from 1st floor, other coming from second floor. 2210 is the current model, its 25" depth.

  10. #10
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,584
    Post Likes
    Quote Originally Posted by a176 View Post
    I had spoken to a contractor who sounded like he was actually giving me good advice and knowledge, and after reading some more after the conversation, I've decided to go with a media filter instead of eac. in regards to this, just a quick question regarding some of the concerns ive read about,

    i have a somewhat entry level furnace, single stage 75k btu, blower rated at around 1100~cfm. The aprilaire merv 11 media is rated at 0.08 IWC drop. will I have an issue with pressure?
    It's rated at; Air Flow @300 Fpm with Initial Resistance @0.08 in WC, Final Resistance @0.5 In WC.

    The filter's free-air-area will put the initial velocity around twice that 300-fpm number.

    A 16X25 filter is 400-sq,ins / 144 is 2.77-sf; * using .65% free-air-area = 1.8-sf.
    1100-CFM / 1.8-sf is 611-fpm velocity through a new clean filter.

    A pleated filter is usually rated at 500-fpm initial velocity; therefore, the pressure drop will be considerable greater than what is stated at 300-fpm.
    AOP Forum Rules:

    Rules for Posting

    Rules For Equipment Owners

    Equipment Owners Find a Contractor HERE!

    Free online whole house load calculator & Sizing: http://www.loadcalc.net/ Anyone can use it...!

    udarrell

  11. #11
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,744
    Post Likes
    Udarrell....I don't think the picture he sent was the AprilAire 2210. I'm assuming that the new filter will be much thicker.

    The 2 returns don't sound like enough. what size are the grilles and where are they located? Floor or wall?

    I have never heard of the 2210...I'll go online and have a look.

  12. #12
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,744
    Post Likes
    I went to the AprilAire website and the model 2210 (media) looks very much like a Bryant/Carrier "E-Z flex" media.

    The site said the maintenance requirerment is 1 to 2 years..............Right!

  13. #13
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,095
    Post Likes
    Quote Originally Posted by George2 View Post
    I went to the AprilAire website and the model 2210 (media) looks very much like a Bryant/Carrier "E-Z flex" media.

    The site said the maintenance requirerment is 1 to 2 years..............Right!
    On a very clean house with no activity.