    we have an older lennox forced air heating furnace.

    the control box has a dial with 2 pointers - one pointing at a high temperature and the other at a low temperature.

    when we moved in here the controller was set to: 200 / 90

    I assume this is the temperature that the burner heats up to and the temperature that the fan turns off at?

    I want to set the temps for the maximum efficiency and least gas useage.

    what do you recommend as the ideal settings?

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    16,446
    Dont fiddle with that, it is a safty control.
    "If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding

  3. #3
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,342
    leave them where they are. one is fan off, other is high limit.

  4. #4
    Join Date
    Nov 2001
    Posts
    1,874
    To get max eff
    You may want to upgrade to a new 90% or 80% with variable speed drive.
    You'll be glad you did.
    If you try to fail, and succeed.
    Which have you done ?



  5. #5
    Join Date
    Nov 2006
    Posts
    16
    thanks toolpusher -

    what does the 80 / 90 refer to?

    and on my original control box - does the 190 limit temp refer to the air temp before the fan goes on, or the constant air temp while it's running, or the temp of the burner, etc?
    and the lower number, 90 in this case, does that refer to the temp at which the fan goes off or on, etc?

  6. #6
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    1,161
    190 is the high limit. If the heat exchanger reaches this temp the burners are shut off. Sounds a bit high to me as it is.

    The 90 is the fan off setting.

    Have the heater inspected by an experienced service tech. He will be able to advise on the settings based on furnace model and operation.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  7. #7
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,131
    Yes, the 200 is the limit temperature. If the limit control ever gets to 200º, it will turn the gas valve off and attempt to run the blower until the limit resets.

    The 90 is the temperature that the control turns the fan off after a call for heat ends.

    From your desctription, and the fact that it is an old Lennox furnace, the control is a Cam-Stat brand fan/limit control, I bet it is 7" insertion too. Since it only has 2 dials, it is a timed on control with 6 wires going to it, so there isn't a dial for the fan on temperature.

    As others have said, don't mess with it.

    If a technician ever has to replace it, don't be to suprised if the replacement looks totally different. While Lennox primarily used Cam-Stat fan/limit controls, the furnaces also have mounting holes for a Honeywell control in the same spot. The important thing is that the replacement be a 6 wire timed on type with about the same insertion depth.