Results 1 to 13 of 17
Thread: heating trouble
    heating trouble
    i have a 48tme012 and the only way that I get the heating call to work is to turn the IDF to on,then eveything will run IDF and burners come on and will cycle on the therm for temp. If fan left in auto the unit will not do anything. I disconected the therm wires at unit and jumped out r-w1 no action but r-w1 and g unit starts. The ignitor module and limin switch were replaced July,2012
    Mar 2010
    Arnold, Mo
    I'm not sure about that unit in particular, but some units must have a G call with W for the furnace to come on.
    Southeastern Pa
    What are the first five digits of the serial number?
    5105G30610
    May 2012
    is there a time delay relay in the unit?
    Dallas ,Texas
    The unit should start in heat mode with a closure for R to W1. We're there any alarm codes blinking on the igc? Is there a basic stat on it or any other controls?
    Southeastern Pa
    Quote Originally Posted by Dallas Duster View Post
    I agree. Power to W1 should start the inducer, and the fan will come on after a time out expires.
    You have something amiss here.
    Southeastern Pa
    Quote Originally Posted by COMFORTHVAC View Post
    I've never seen a module in a 2005 Carrier RTU. Can you post a pic?
    AND...
    Have you inspected that heat exchanger??????
    Oct 2011
    Chicagoland Area
    I'm curious as to why the igc board and limit were replaced in July. Were they causing issues in a/c mode?
    Local 597 Service Fitter
    Metal Trade Journeyman
    PAY ME NOW OR PAY ME LATER
    It was working when I left...
    WWFD
    THERE WAS A PROBLEM WITH THE A/C IN JULY AND AT THAT TIME THE INDUCER WAS RUNNING ALL THE TIME LIKE THE ROLL OUT WAS OPEN BUT IT WAS NOT BUT FOR THE PRICE OF THE ROLL OUT I REPLACED IT WITH THE CONTROL. IT HAS A W/R TWO STAGE HEAT AND COOL THERM.
    Oct 2011
    Chicagoland Area
    Once the igc goes into lockout the inducer stays on even after the limit becomes closed. This would have been indicated by the flashing red light. Next question. You said you disconnected the t-stat and then jumped out. Was this done at the unit or inside by the thermostat?
    WWFD
    I jumped at the unit. r-w1 no change have to jump r-g once the r-g jumper is touched you can remove the jumper and just leave the r -w1 and the unit will keep on running.
    Dallas ,Texas
    What is the complete 16 digit model number?