    nordyne tripping limit

    model m3rl080a
    ser m3a050301139

    keeps tripping limit on combustion blower
    work alright while i there
    something over heating but what
    any help?

  2. #2
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    is this a 90%?

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by iowa tech View Post
    model m3rl080a
    ser m3a050301139

    keeps tripping limit on combustion blower
    work alright while i there
    something over heating but what
    any help?
    I would first pull the inducer motor off and check to see if the restrictor plate (inducer orifice as they call it) is damaged, eaten away, or has fallen out.

    If the inducer is pulling too much flue gas through the orifice, the gas is not having enough time to cool off by staying in the HX long enough.

    You can also put a temp probe in to see if the flue temp is above 145ºf to eliminate the possibility of a bad switch.

    The part number for the orifice on the 80,000 btu unit is #155315R.
    Instead of learning the tricks of the trade, learn the trade.

  4. #4
    Join Date
    Nov 2005
    Posts
    367
    Post Likes
    Thread Starter
    Temp is about 135 in flue
    New c blower install by first tech
    Yes 90%

  5. #5
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by iowa tech View Post
    Temp is about 135 in flue
    135ºf flue temp is tripping a 145º limit.

    How far away from the inducer did you measure the temp?

    Assuming you are confident of your temp reading, and the 135ºf flue temp is stable, I would be installing a new limit.

    A combustion analysis would help in determining if the readings are stable.
    Instead of learning the tricks of the trade, learn the trade.

  6. #6
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    Post Likes
    i remember my first time with a problem similar....the disc was so rotten that it wasnt there. i was pulling my hair outa head untill some other guy said that the opening should be 1.5 inches.....i said its about 3.... disc wasnt even there or any signs of it...hahahaha

    couple months later i go to similar call....new apprentice was like omg u so smart...lol i told him the long version....he laughed....


    Please, Please Please......keep the Factory Smoke in the Wires!!!!!


    Is it Rum'Oclock yet???

  7. #7
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    135* flue temp.

    combustion analysis would help determine whats going on. 135* is max you want on a 90% furn

    check air supply blower wheel and secondary heat exchanger. Make sure your moving enough return air. usually low airflow or overfired causes flue temp to be that high.

    you need 150cfm per 10,000 input btu with 90% furnace.

  8. #8
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by BigBacardi View Post
    i remember my first time with a problem similar....the disc was so rotten that it wasnt there. i was pulling my hair outa head untill some other guy said that the opening should be 1.5 inches.....i said its about 3.... disc wasnt even there or any signs of it...hahahaha

    couple months later i go to similar call....new apprentice was like omg u so smart...lol i told him the long version....he laughed....
    I find a lot of these m3 furnaces with inducer limit tripped. To date, every one was due to corroded or missing orifice.

  9. #9
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    I find a lot of these m3 furnaces with inducer limit tripped. To date, every one was due to corroded or missing orifice.
    Invaluable information, thanks, hear of this one time only but the other tech never found the issue that I know of.

  10. #10
    Join Date
    Jan 2011
    Location
    Ottawa, Canada
    Posts
    470
    Post Likes
    Orifice.. one for the memory banks...

    Sent from my SGH-I747M using Tapatalk 2

  11. #11
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    The older Lennox ghr 26 had them also.

  12. #12
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by Joehvac25 View Post
    The older Lennox ghr 26 had them also.
    Yes. Did you ever see one of those corroded? They obviously used better material.

  13. #13
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    Yes. Did you ever see one of those corroded? They obviously used better material.
    No but I have seen the condensate box come apart and not close ps switch. Inside of it i mean. The old discs always seem fine in the inducer!

  14. #14
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Quote Originally Posted by Joehvac25 View Post
    Invaluable information, thanks, hear of this one time only but the other tech never found the issue that I know of.
    you do mean valuable?

  15. #15
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Quote Originally Posted by gravity View Post
    you do mean valuable?
    "invaluable
    in·val·u·a·ble
    adjective beyond calculable or appraisable value; of inestimable worth; priceless"

    Valuable/invaluable - the same
    Flammable/inflammable - the same
    English is weird.
    Last edited by kdean1; 11-09-2012 at 09:52 PM. Reason: clarifying

  16. #16
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Lol I guess what I meant was invaluable as in so useful you can't put a price on it, seems like I heard that expression somewhere but maybe I got it wrong. So yes unmeasurable value.

  17. #17
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    thank you kdean and joe.

    the English language is pretty jacked up.

    to, too, two, there, their, they're.....etc

  18. #18
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Never would have crossed my mind. How many furnaces have this "restrictor plate"?

    This site is unvaluably inmeasurable.

  19. #19
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by hurtinhvac View Post
    Never would have crossed my mind. How many furnaces have this "restrictor plate"?

    This site is unvaluably inmeasurable.
    Lol

  20. #20
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by hurtinhvac View Post
    Never would have crossed my mind. How many furnaces have this "restrictor plate"?

    This site is unvaluably inmeasurable.
    Every nordyne furnace has one since they all use the same inducer (within a model series). A 60k btu will have a restrictor with a small hole, while a 120k will have one with a big hole.

    The faulty restrictors seem to be on models made in the early to mid 2000s. They were made from an opaque plastic that flakes away. The problem is most pronounced on units where the filter was not changed often enough.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •