Results 1 to 6 of 6
    Jun 2005
    HELP! Comtrol 4K rack controller
    Im working on a hussmann rack that is controlled by a Comtrol 4K. I am not too familiar with these and does not help that the screen is blanked out. Where can I get a new one of these or can I just replace the screen? I think that the suction transducer is reading high, cause the controller is running the rack about 8# too high.. making my meat cases run lil warm. I cannot verify that with the screen being out. I dont have a spare transducer either.. maybe that would be the better route? The customer has seen the controller and would fix/replace it though..
    Jan 2010
    Sea to Sky
    Why is the screen blanked out? No power to it? Physical damage to the screen?
    Jun 2005
    Actually blanked out wasnt a very correct description.. The screen cannot be read. There are dashes and lines all over that prevent reading any value or seeing screen options:/
    California
    Comtrol is no longer in production.
    you would be better served looking into an E2 or a Danfoss controller.
    They both have provisions to accept the existing Comtrol IO network.
    That way, you are at least making a move forward.
    Chino, CA
    there is a dial in the back where you can adjust the contrast maybe it will help some. is there a 5k(modem for Comtrols) in the store you can connect to using ezcom and you can see what your controller is doing.
    Cochrane, AB
    If you are working at a Safeway store the head office will have a surplus supply of used 4K controllers. If not, then E2.