Honeywell T7350 Temperature jumps around
If you're wondering, it's the same job...
A Honeywell T7350 tstat with the remote TR21-H Temp/Humidity sensor... The original complaint was the temperature was jumping around by 3-5 degrees, and that the humidity wasn't working. Took a new sensor to the site, and found the old sensor had a very obvious burn mark by the 24V input connector. Swapped out the sensor, and the humidity now works, but the temperature is dancing around by 1-3 degrees.
My thinking is whatever killed the humidity side of the sensor, might have went back up the temperature sensor signal wire, and screwed up the stat.
Going to go out to the site this afternoon and swap sub-bases, but wanted to see if anyone had any insight as to what might be wrong?
The customer said he put a regular temp sensor on the temp line, and it worked fine. We put a brand new temp/humid sensor on, and it doesn't????NeonHomer
The definition of cruel joke is when you start work in BAS, and you run into your old T&B employer on the job.
-
10-04-2012, 10:50 AM #2
Swapped sub-bases... Temp still jumps around.
Only thing I can think of now is that maybe the wire is bad, or it is picking up noise,.,..,.,NeonHomer
The definition of cruel joke is when you start work in BAS, and you run into your old T&B employer on the job.
-
10-04-2012, 04:52 PM #3
Professional Member
- Join Date
- Jan 2006
- Location
- Sydney Australia
- Posts
- 67
if you have devices sharing the same 24V power, try making sure they are all wired to the same terminals and not crossed.
read the install manual for device and follow it.
hope this might help, its all i got
-
11-08-2012, 04:00 PM #4
New Guest
- Join Date
- Sep 2012
- Posts
- 3
This may be unrelated, but the T7350 head and subbase are a matched set. We have seen various issues arise when an old subbase is attached to a new head and vice versa.
-
11-08-2012, 09:31 PM #5
Sounds like noise to me. Have seen this before. Re-wired with shielded wire and routed away from several romex runs to solve the problem.
"Controls is a lifestyle not a job" -klrogers