    fan limit control
    Just installed a thermo pride oil furnace ,what settings do you set up for the on and off on the fan control ,installed late last night ,going back to finish later in week ,heavy furnace, Thanks
    Jun 2012
    Fayetteville, NC
    The limits should already be set. What does the install manual say?
    SE Michigan
    Shouldn't have to mess with it.
    Apr 2012
    winnipeg
    yep
    Jun 2007
    140 on, 90 off upflow
    120/80 downflow
    I would not set off any lower than 100° at the register or you most likely will get a call about it.
    most likely it is already set, as has been said.
    mfr should list limit, usually 200°.
    on/off temps should be far enough apart to keep short cycling from occurring.
    Jul 2003
    The limit temp. varies. It's in the manual. around 190. call me at Tech support if you have any problems with start up