Originally Posted by
JBocc
As suggested by DogBoy in his last thread on this topic I am providing an update and what i feel is the solution this problem.
First.... I am most certain at one point I was dealing with two issues. The first was Problem A the overheating with out a call for heat. Then I find problem B which was W and O present giving the compressor lockout fault codes shifting to emergency heat and causing the problems as previously posted. Correct Problem B thinking I got it ....but oh no Problem A comes back some 20 days and this time it finally clicks that this is happening when ambient is below BP.
I spoke with both Honeywell and York again... I 'll break out each their points below
YORK
Given that the defrost control board in this heat pump controls the staging of W1out and W2out to the A/H W1 and W2 based on BP and LTCO setting. It was felt it would be best to disable the same functional control that was set up the zone panel to lock out the aux heat until below 35 ( same as BP setting in Heat pump defrost board). and just let heat pump control stage W1 and W2. A call for compressor on Y in conjunction with W ( based on BP will or will not energize W1 and after 15 min w2) A call on W without a compressor is acknowledged as emergency heat and w1 and w2 are energized as required.
After a Q&A with my 3rd honeywell tech on this problem and explaining what I described above I asked him to explain the out put signals. He stated to me that W1/E only energizes on a aux/emergency heat call and w2 energizes on a aux/supplemental call with compressor. That caught me off guard and I asked him to repeat it and I wrote what he said to be sure I heard him right .He suggested I remove the jumper on the zone panel and wire w2 to the defrost control board...what about the emergency heat call as it goes thru the defrost control board??? the jumper remains in place.
Trying to incorporate the zone panel lockout and trying to utilize the rudimentary wiring diagram of the installation manual I wired w2 from the panel to w2 on the AH in conjunction with w2 coming from defrost control board...so I must of had a emergency heat signal and a supplemental heat signal at the same time below BP . That must have caused a back feed to latch the dry contact closed even though there was no call for either heat
so today
I disabled the zone control aux heat LO
removed the w2 to w2 wire
test all functions above and below BP based on todays ambient
I feel pretty good about this.... feel like a bit of a dumb ass as well. my other zone jobs went off with out a hitch but I second guessed the little voice when I was wiring this as I could not find my reference drawing from the previous installs