Thread: Carrier Infinity Stat.
-
11-05-2012, 09:15 AM #1
Carrier Infinity Stat.
My in-law has a 3 years old Carrier Infinity system. Last fall, they mention to me the stat screen was showing "Emergency Heat" on the screen.. I go and check it and sure enough it was showing that... So I go into the advance setting menu to see what's going on, and all is normal.. When I go back to home screen "Emergency Heat" then goes away.
We were there yesterday, and she said it's doing it again.... I go check all settings, and nothing is set up as a heat pump.. Just an infinity furnace and A/C.
The system works just fine....
-
11-05-2012, 03:04 PM #2
Professional Member
- Join Date
- Dec 2011
- Location
- missouri
- Posts
- 135
I'm not sure if there is a difference between infinity and evolution( Bryant's version), but they did have a problem with the UI loosing its memory. I believe it was on the version 16 and older. If power was interrupted, they would not hold their settings and go back to factory defaults. If the date , and time are not right, or have changed, that may be your problem. Have you tried re-installing equipment in "service" under " advanced settings"? Hope this helps
-
11-05-2012, 03:51 PM #3
Professional Member
- Join Date
- Jun 2012
- Location
- Fayetteville, NC
- Posts
- 123
Version 16 has a problem with memory. it gets too full to quick. You probably need to switch it out with an updated software version
-
11-05-2012, 04:06 PM #4
-
11-06-2012, 11:08 PM #5
Professional Member
- Join Date
- Feb 2012
- Location
- Tennessee
- Posts
- 52
Normally if a t stat says its in emergency heat it has to be set up as a heat pump a straight air with furnace would not have e heat
-
11-07-2012, 08:50 AM #6
Hold the red button down for several seconds and an option will appear to change from emergency heat to heat pump/furnace.
Check page 10 of the attached link. It's actually page 7 of the document.
http://www.docs.hvacpartners.com/idc.../OMUID-3CA.pdf


Reply With Quote