Page 2 of 2 FirstFirst 12
Results 14 to 16 of 16
  1. #14
    Join Date
    Feb 2004
    Posts
    2,789
    Post Likes
    Sounds like you have a classic "floating" flame. Poor venting, clear the HX of crap. It is restricted and not allowing the products of combustion to vent and the flame is recirculating seeking combustion air. Anyway that's what it sounds like.

  2. #15
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420
    Post Likes
    Quote Originally Posted by mike3 View Post
    Sounds like you have a classic "floating" flame. Poor venting, clear the HX of crap. It is restricted and not allowing the products of combustion to vent and the flame is recirculating seeking combustion air. Anyway that's what it sounds like.
    yea, pull the draft hood and look thoroughly at the top of the heat exchanger, could have a bird in it. Have you tried swopping burners to see if its the burner or if its that section of the heat exchanger
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  3. #16
    Join Date
    Aug 2010
    Posts
    5
    Post Likes
    Thread Starter
    Thanks to everybodies replies I was able to fix it. I had to take the draft hood off and and remove metal pieces inside hx. After cleaning and vaccuming out upper hx the burners were fine. This website rocks! Thanks guys.