Sounds like you have a classic "floating" flame. Poor venting, clear the HX of crap. It is restricted and not allowing the products of combustion to vent and the flame is recirculating seeking combustion air. Anyway that's what it sounds like.
-
11-13-2012, 03:10 PM #15As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84
-
11-23-2012, 01:14 AM #16
New Guest
- Join Date
- Aug 2010
- Posts
- 5
Thanks to everybodies replies I was able to fix it. I had to take the draft hood off and and remove metal pieces inside hx. After cleaning and vaccuming out upper hx the burners were fine. This website rocks! Thanks guys.