    Old Trane burner problem

    I am working on a old standing pilot Trane BLU120E936B. The burners are in suprisingly good shape. There was some debris on them....like some white little foam balls???...some rusty powder inside them. They were'nt that rusty in the slots. So I cleaned them. It has four burners, and one of the middle ones will lite the length of the burner, then after a few seconds, slowly go out until it comes back to where there is a small ball of flame next to the crossover part of the burner next to the pilot. I adjusted manifold press from 2.5 w.c. to 4 in , recleaned burners, cleaned crossovers, adjusted pilot, checked orifice and it was clean. Any suggestions? BTW...the other burners are burning fine, and from what I can see my problem burner looks fine???

  2. #2
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,394
    Nat or LP?

  3. #3
    Join Date
    Nov 2006
    Location
    Wisconsin
    Posts
    293
    If the "ball of flame" is by the pilot assembly, I'm guessing its either the pilot flame itself, or the pilot assembly is in the path of the burner flame and disrupting it. How big is your pilot flame? As far as the manifold pressure, 4.0 sounds more like a boiler setup than a furnace. If it is a furnace it should be 3.5 if this is a natural gas unit. Also check for Flame distortion on blower start-up if it is a furnace

  4. #4
    Thanks to everybodies replies I was able to fix it. I had to take the draft hood off and and remove metal pieces inside hx. After cleaning and vaccuming out upper hx the burners were fine. This website rocks! Thanks guys.

  5. #5
    Join Date
    Dec 2011
    Location
    missouri
    Posts
    186
    I would check for s spider nest in the manifold. It sounds like that burner is starving for some reason.

  6. #6
    Check the orifice ther might be a retriction and adjust your manifold press to 3.5 w.c. Also your burner holes may still have build up off that white powder

  7. #7
    Join Date
    Jul 2010
    Location
    Eastern Kentucky
    Posts
    55
    Is that part of the heat exchanger above that burner stopped up?

  8. #8
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,412
    Make sure the ribbon isn't clogged. Make sure the burner orifice doesn't have a flake of metal stuck in it.

    make sure that cell of the heat exchanger is clear.

    very interesting call. hope you figure it out. let us know what it is.

  9. #9
    How do you check if the cell of the heat exchanger is clear?

  10. #10
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,412
    you could also have a big crack in that cell. does it do this when the blower comes on?

  11. #11
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,858
    Quote Originally Posted by mprob View Post
    How do you check if the cell of the heat exchanger is clear?
    As gravity said, visual inspection.

    Either remove the flue box cover or pull the burners, and stick an inspection scope in each cell.

    At 25+ years old, and with the problem you are describing, my money is on the HX has been compromised.

    I would also want to do a combustion analysis on that unit before I put it back into service.
    Instead of learning the tricks of the trade, learn the trade.

  12. #12
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,412
    light test. visual inspection. you may have to take off the collector box

  13. #13
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,412
    Sorry to hi-jack.

    Rundawg...Did u make the powerpoint of checking static pressure?

    There is a thread in the tools. Guy wants to know how to check it.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event