    Water Source HP condenser flow issues

    I have a new 2 ton mcquay wshp that has an air delta T of 10 deg. and a condenser water delta T of 25 deg:
    return air 72 supply 62
    supply water 75 return 100
    r410a low 130~45 deg high 350~106deg.

    My first thought is to flush the condenser loop in the unit, there are no strainers or flow-raters around the unit and it is on a closed loop system. Beyond that, I was advised by a trusted supervisor to switch the 1/2" steel braid hoses (which is the standard for the unit, per the product literature) to 3/4", leaving the 1/2" piping from the main supply line to the unit. If a gummed-up condenser coil is not the issue, will the increased hose diameter increase the water flow, even if the unit is designed for 1/2" and the piping is 1/2" as well?

  2. #2
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Is there multiple units on this condenser loop? What head pressure are they running?

  3. #3
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    I don't think the 3/4" hoses will help.

  4. #4
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    31
    Post Likes
    Thread Starter
    there are about 60 similar hp's on the system. no problems with HP over the summer in any units in occupied suites. The one in question is in a vacant suite. When I originally looked at it for the management who want to lease the space it was off on a HP fault. resetting the unit didn't erase the fault. checked the HP switch, it was closed. Replaced the circuit board and the unit ran. I will check the pressures on some of the nearby units. I'm hoping the flush will produce something. If not maybe a booster pump is necessary.

  5. #5
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    31
    Post Likes
    Thread Starter
    results:
    flushed condenser, cleared some crud from it, water split went down a few degrees
    changed hoses, water went down a few more degrees, now the split is 17 deg. 75/92 deg
    pressures went down a little but they seem to be normal 125/320 psi (43/100)
    air split is still low 67/59 in cooling, but higher 83/99 in heating. also, the pressures don't change in heating mode.
    the two units just upstream in the loop, one has a normal water split 8 deg., one is a little high 14 deg.
    another unit next door on another branch (same loop) has a normal water split as well (10 deg)

  6. #6
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Your condenser delta should average 10 degrees I think you water flow is low a gummed up condenser should show a lower delta T.

  7. #7
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    ANYBODY who installs a closed loop condenser system and does not install local strainers on the inlets is "Cheating" and this is the end result.

    How was the system ever balanced without circuit controllers? This blows my mind....

    IMHO you should have flow devices and strainers on every unit you touch. Otherwise you will just be chasing the problem around like a Super ball in a gymnasium.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  8. #8
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Do you have IOM for this unit? It should state the minimum gpm required. You could disconnect waterline and see how long it takes to fill a 55 gal drum. Then calculate gpm.

  9. #9
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    Look in the IOM for the unit, there should be a chart to show pressure drop on the heat exchanger so you can calculate GPM..

  10. #10
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    31
    Post Likes
    Thread Starter
    i would love a wye-strainer and a pressure tap on the shutoff. unfortunately, this is a 30 yr old system with PVC piping and leaky gate valves. at least this one has ball valves (PVC ones). First thing i did was look up the manual (installer was nice enough NOT to leave it) and found the GPM is 6.4. I like the fill the drum idea, maybe 2 5 gallon buckets would be more practical?
    also, don't these pressures seem correct for the system? I was told 10-12 degree above condensing water temp for the head pressure in water cooled system. i am wondering if there are air flow problems. i did find that the IBM was wired for the wrong speed, but i corrected that first.

  11. #11
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    31
    Post Likes
    Thread Starter
    oops I was using the return water temp. when i was thinking the head pressure was correct instead of the supply. the supply temp is 75 deg so i guess the head pressure should be 256

  12. #12
    Join Date
    Jul 2008
    Location
    Mid Michigan
    Posts
    321
    Post Likes
    Is your water line big enough to feed all of the heat pumps in the loop. By the way they all need strainers and h2o circuit flow control.
    What is the GPM for the unit you are working on, it may be more than the other units already in the system
    Waddya mean don't thaw out the frig with a knive?

  13. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by socotech View Post
    ...You could disconnect waterline and see how long it takes to fill a 55 gal drum. Then calculate gpm.
    this will not come even close to measuring the gpm of the system. an open line is very different from a closed loop with pressure reductions.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  14. #14
    Join Date
    May 2007
    Location
    Boise, Idaho
    Posts
    118
    Post Likes
    I like the fill the drum idea, maybe 2 5 gallon buckets would be more practical?


    Doesnt work like that with an open pipe, there is no pressure on it so that would be free flow. You must have a way to test pressure drop across the water coil and manuf. specs to calculate GPM PERIOD!!! Anything other than that is a guess at best. Remember the water outlet has pressure on it too. EVERY manuf. out there has these specs available.

  15. #15
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Those braided hoses you mentioned have a rubber lining inside the deteriorates over time. I'm betting you still have a fouled condenser. You do need the h2o circuit setters and strainers. It would be a good investment.

  16. #16
    Join Date
    Jun 2008
    Posts
    9
    Post Likes
    Check ball valves for in-line screens. I had a supply ball valve with a clogged screen in it. Not the strainer style. Just a small screen similar to one you see on a faucet.

  17. #17
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,077
    Post Likes
    JayGuy stole my thunder as he is correct. System friction on supply and return affect flow so the open bucket trick proves nothing.
    It might get loud!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •