What size portable generator for my Lennox G71V Furnace?
I am going to purchase a portable generator for a few items in my home in the event of power failure. How much power will it take to run my Lennox G71V 110,000 Btu Gas Furance with ECM motor. I utilize this furance in 2 stage mode and not in modulating mode. Stage 2 for heat puts out about 1550-1600 cfms, however it very rarely gets out of stage 1. I will not be using the generator for my AC.
Thanks.
-
11-05-2012, 11:53 PM #2
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,269
I did not discover the exact G71V spec required, but G61MP requires up to 1400 watts.
See page 50
http://www.lennox.com/pdfs/installat..._G61MP_IOM.pdf
See page 51
http://www.lennox.com/pdfs/installat...G71MPP_IOM.pdfDesigner Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
11-06-2012, 06:21 AM #3
You need a good generator with clean juice to run today's electronic furnaces. There's another board with many northeast members and there's been a lot of dicussion about this. Some were not able to get their modern products to work on their generators due to the quality of the AC current.
-
11-06-2012, 06:54 AM #4
Regular Guest
- Join Date
- Aug 2009
- Posts
- 154
I was looking into buying a Winco tri fuel 5000 continuous watt portable generator run on natural gas. My other option us a 20kw Kohler whole house generator, but the cost is very high. Was hoping to find a quality option for a reasonable cist.
-
11-06-2012, 08:34 AM #5
There are options in between. Standby generators come in smaller sizes. You could get a 8KW genrators and run just the furnace and critical appliances like fridge and maybe 1 wall outlet for a toaster oven or microwave and a couple ligting circuits. They also have smart switches which can cycle various circuits based on demand. If I understand them correctly, it might allow for example allow you run the AC, but not the refrigerator at the same time, or run 1 AC at a time if you have 2. Even in this very hot July, in my larger home with 2 AC's, I still only averaged around 2.2kw-hrs. Take the oven and an electric clothes dryer out of the equation, and you peak requirments drop quit a bit.
Carrier Infinity for example allows a remote input to disable 2nd stage as well. That would limit the running load to I think around 1500W or less on a 2 ton unit. IT definitely pays NOT ot have an oversized AC when your tryign to pair it with a standby generator.
-
11-06-2012, 12:38 PM #6
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,616
as long as it's a quality standby generator, not a portable cheapo, it will handle the load of any basic furnace under 3 tons of blower capacity. above that, the 115V blower motor will pull too high a load on the generator unless you go over 10KW.
forget trying to start an air conditioning system with less than 15KW there are just not enough surge amps available to start the compressor.The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman
-
11-06-2012, 09:07 PM #7
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,269
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities