    Quote Originally Posted by Phase Loss View Post
    This is embarrassing I never gave much care for glide

    Just hooked up my digi's and it did the work for me never really looked at a PT chart with vapor/liquid pressures.

    makes me think back a few years ago, back to a chain of stores my old company used to service.

    Each case used a case controller that used a pulsing metering device that based superheat off of coil inlet/outlet temperature difference.

    Each store was R-404A and worked well.

    Then they put in a 407C store...and it was oil fail central.

    This actually proves a point I tried to make a few times and got slammed for it.... Glad you knew the manifold set was smarter than you were....

    Not being condescending, just appreciating you know the difference.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  2. #15
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    I knew it read dew/bubble point...so I never cared to look into it


    technology made me lazy & stupid there.

  3. #16
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,790
    Quote Originally Posted by Capz View Post
    I also use the Fluke 52-2 with the K thermocouple wire probe and some foam or cork tape. I was just curious to know if anyone had a better method for temperature accuracy
    Cooper 4011 fits great on the little tubes well as suction lines or return bends.
    Much easier/better than the beaded K-Type IMO
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  4. #17
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,790
    Phase Loss This might help it sink in. This was on a unit overfeeding. In the pic it shows bubble, dew for the pressure and suction temp.
    It's easier for me to grasp glide when seen this way vs pt charts and graphs but maybe somebody has a better way of explaining glide. HTH
    Attached Images Attached Images  
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #18
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    The impossible negative superheat scenario. DUN DUN DUUUUNNNNNNNNNN

  6. #19
    Join Date
    Oct 2010
    Posts
    14
    Quote Originally Posted by Capz View Post
    I also use the Fluke 52-2 with the K thermocouple wire probe and some foam or cork tape. I was just curious to know if anyone had a better method for temperature accuracy
    Try the fluke 80pk-3a touch probe. I have several of the fluke temp clamps, but like the touch probe best.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event