Results 1 to 12 of 12
    Mar 2011
    Georgia
    Confused 5 Min delay problem.
    I am a AC tech & trying to fix someones heat pump but it has a very strange problem.
    It runs fine in cool mode but in heat it gives problems.
    We just installed the unit last year its a RUUD value series 3 ton heat pump R410A the Air handler was a couple years old R410A model.
    The TXV sensing line bulb in the heat pump had broke and I brazed it back not wanting to start replacing parts if its not going to be the only problem.
    The pressures were giving me problems so I stated off replacing the evap coil TXV first. Now they seam fine, but when I start in heat mode it runs for around a min but compressor starts clicking and shuts off.
    Then it shows 5 min. delay on the board I have bypassed the low & high pressure switches and still does it. Pressures are 375 hi & low.
    I have never seen 5 min delay pop up for a error. And yes it keep the control voltage to the board the whole time for it to run.
    I'm just wanting to know could the TXV be the problem or maybe the board?
    Or any other idea's ?
    Southeastern Pa
    We probably can't address these technical matters in an open forum. Get your post count up to 15 and apply for pro membership.
    Mar 2011
    Georgia
    OK thanks. I wasn't sure.
    I'm just trying to get these peoples heat working and my boss is out of ideas.
    Bypassing switches not a good idea, brazing sensing bulbs not a good idea. Your main problem might be with the air flow in your air handler. you need to check your sh and sc along with w.c.
    MN
    I'm curious as to how you recharged the bulb?
    Mar 2012
    West Chester, PA
    Well the TXV isn't going to have anything to do with that. I would guess you are losing power to the board or dipping below the minimum voltages required to power the board or initiate a call or a float/wet switch is cutting in and out or you have a broken wire which is making intermittent connections...
    Jun 2006
    Richmond, VA
    Quote Originally Posted by ADillon View Post
    Yes it will if its in the outdoor unit and having problems in the heat mode....and like a previous poster said and I am curious too......"how did you recharge the bulb"
    It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!
    Jun 2011
    Muncie, Indiana
    You provided enough info in your post to figure it out. Think about what the out door txv does and then think about what would happen if it wasn't sensing.
    The only true knowledge is the pursuit of knowledge
    Jul 2010
    Eastern Kentucky
    Sensing bulb line broke on TXV? Maybe you are talking about external equalizer line?. 375 psi on high and low side? put your low side gauge on dedicated suction line and see what you have
    Quote Originally Posted by camarofreak View Post
    The pressures were giving me problems so I stated off replacing the evap coil TXV first. Now they seem fine
    Now go replace the TXV you repaired the bulb on ( you cannot repair a sensing bulb because inside that bulb is a special gas , until its broken ) ... oh and put your guages on the correct ports when in heat mode.
    Mar 2011
    Georgia
    I Did end up Replacing the TXV. And it fixed the Problem.
    Thanks for the info.
    First time I have had a problem with outdoor TXV. My boss kept telling me that was not the problem & it needed R410
    And as far as the bulb goes he told me that he had brazed the line before to repair it.
    But i'm pretty sure it was the piston type.
    I have only been doing this 2 years and no school just was showed how to do a few things then sent out on my own to figure out the rest. Hoping to learn more from you guys.
    Southeastern Pa
    ...which is why you need Pro membership, so we can help you in the closed forums........