5 Min delay problem.
I am a AC tech & trying to fix someones heat pump but it has a very strange problem.
It runs fine in cool mode but in heat it gives problems.
We just installed the unit last year its a RUUD value series 3 ton heat pump R410A the Air handler was a couple years old R410A model.
The TXV sensing line bulb in the heat pump had broke and I brazed it back not wanting to start replacing parts if its not going to be the only problem.
The pressures were giving me problems so I stated off replacing the evap coil TXV first. Now they seam fine, but when I start in heat mode it runs for around a min but compressor starts clicking and shuts off.
Then it shows 5 min. delay on the board I have bypassed the low & high pressure switches and still does it. Pressures are 375 hi & low.
I have never seen 5 min delay pop up for a error. And yes it keep the control voltage to the board the whole time for it to run.
I'm just wanting to know could the TXV be the problem or maybe the board?
Or any other idea's ?
-
11-05-2012, 09:04 AM #2
We probably can't address these technical matters in an open forum. Get your post count up to 15 and apply for pro membership.
-
11-05-2012, 09:20 AM #3
Regular Guest
- Join Date
- Mar 2011
- Location
- Georgia
- Posts
- 6
OK thanks. I wasn't sure.
I'm just trying to get these peoples heat working and my boss is out of ideas.
-
11-05-2012, 10:13 AM #4
Bypassing switches not a good idea, brazing sensing bulbs not a good idea. Your main problem might be with the air flow in your air handler. you need to check your sh and sc along with w.c.
-
11-05-2012, 03:40 PM #5
I'm curious as to how you recharged the bulb?
A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii
-
11-05-2012, 03:43 PM #6
Well the TXV isn't going to have anything to do with that. I would guess you are losing power to the board or dipping below the minimum voltages required to power the board or initiate a call or a float/wet switch is cutting in and out or you have a broken wire which is making intermittent connections...
-
11-05-2012, 04:13 PM #7It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!
-
11-05-2012, 05:01 PM #8
Professional Member*
- Join Date
- Jun 2011
- Location
- Muncie, Indiana
- Posts
- 224
You provided enough info in your post to figure it out. Think about what the out door txv does and then think about what would happen if it wasn't sensing.
The only true knowledge is the pursuit of knowledge
-
11-05-2012, 07:22 PM #9
Sensing bulb line broke on TXV? Maybe you are talking about external equalizer line?. 375 psi on high and low side? put your low side gauge on dedicated suction line and see what you have
-
11-09-2012, 06:51 AM #10
-
11-23-2012, 04:52 PM #11
Regular Guest
- Join Date
- Mar 2011
- Location
- Georgia
- Posts
- 6
I Did end up Replacing the TXV. And it fixed the Problem.
Thanks for the info.
First time I have had a problem with outdoor TXV. My boss kept telling me that was not the problem & it needed R410
And as far as the bulb goes he told me that he had brazed the line before to repair it.
But i'm pretty sure it was the piston type.
I have only been doing this 2 years and no school just was showed how to do a few things then sent out on my own to figure out the rest. Hoping to learn more from you guys.
-
11-23-2012, 08:24 PM #12[Avatar photo from a Florida training accident. Everyone walked away.]