Thread: Grounded Copeland Hermetic New Install

  1. #1
    Join Date
    Dec 2009
    Posts
    26
    Post Likes

    Grounded Copeland Hermetic New Install

    2 months ago I installed a 1HP 3Ph 404a walk in cooler. I did a test run for 2 days, no problem. Unit was shut down, today construction of restaurant is over and inspector coming tomorrow (health inspector). Owner turned all the stuff on but the cooler didn't work. I found the compressor grounded, what did it? I shut it down (2 months ago) from a pump down switch inside the cooler that shuts down the solenoid and fans. In the mean time we had a bad storm around here, but owner said they didn't lose power. I will replace compressor in the morning, but I just don't want to believe that **** happens. So, any suggestions? Voltage is good all across, protector was opened and never reset itself, I bypassed it to see what happens, nothing happened, I was getting voltage all across 3 terminals but no amperage, that's what makes me scratch my balls, breaker didn't trip, all connections tight, no acid, I kicked (boot kicked) the compressor, checked for ground and now was no more. I checked resistance and I had none across 2 winding terminals (must've moved brains out of the comp with my kick). What happened here? What caused it to get grounded in off cycle? Any suggestions would be nice, would really jump start my brain, I ran out of ideas, Thanks and cheers guys.

  2. #2
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    it happens..... single phased maybe.... who knows......
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  3. #3
    Join Date
    Dec 2009
    Posts
    26
    Post Likes
    Thread Starter
    Here is what I found: at the compressor we have black yellow red terminal wires. the black goes through an external overload, there is also an internal overload. I followed the wires to the main electric panel. This is a 3 phase panel feeds are black red blue. What I did find was at the breaker the wires didn't correspond to right color: had red to black, white to blue, black to red. I rewired the breaker so I have from the main feed black to black, red to red, blue to yellow all the way to the compressor. I have to learn more about the phase thing (panel wise), but so far I believe that was what went wrong, wrong voltage to compressor winding, like I said, I have to look more into this for the future, any suggestions? I replaced compressor and it runs as was intended to, nice all around.

  4. #4
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Coplawelds recips can run either direction. Coplamatic, I believe, can run in either direction too, but once run in one direction, it doesn't do well when reversed.

    Copelawelds depend on refrigerant to cool the motor,coplamatic doesn't. So extended pump down will overheat the motor. Maybe a leaking solenoid?

  5. #5
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    615
    Post Likes
    Quote Originally Posted by Royal241 View Post
    Here is what I found: This is a 3 phase panel feeds are black red blue. What I did find was at the breaker the wires didn't correspond to right color: had red to black, WHITE TO BLUE, black to red.
    So maybe you didn't have three legs of power to the compressor but possibly two power legs and a neutral?
    How many wires in the panel?
    3 or 4?
    What is the voltage measurement from each leg to ground?
    Red to Ground = ?

    Black to Ground = ?

    Blue to Ground = ?

    White to Ground = ?

    The reason I ask is that if someone played with the power at the panel and switched a powerleg for a neutral, then the compressor pumped down due to eventual pressure buildup to activate the pump down circuit/LP Control, compressor could have single phased and possibly shorted to ground.
    It's a stretch but the "white to blue" statement has me wondering...:what:

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Moved thread to refrigeration and Ice making.



  7. #7
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by koolkahuna View Post
    It's a stretch but the "white to blue" statement has me wondering...:what:
    I see what you're saying but if sparky lost some other color phase tape then you get the "that'll do" card.

    If you truly think it was a power issue and want to make sure it doesn't happen again, add a phase monitor to it. Won't take very long and save you a ton of headache.

  8. #8
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    Quote Originally Posted by Royal241 View Post
    Here is what I found: at the compressor we have black yellow red terminal wires. the black goes through an external overload, there is also an internal overload
    So the external overload only breaks one leg of line voltage to the compressor? That doesn't seem right. Normally an external overload has sensors that trip it. Once tripped it will open the control voltage to the contactor, which in turn opens 2 or 3 legs.

  9. #9
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    3p 208 I am assuming? I do not think what you found is the issue. L1, L2, L3 can be wired in any order at the compressor so why would changing the wiring at the breaker make a difference? In addition, you are saying you have a grounded compressor. But you are not tripping the breaker. What is the resistance reading from the motor legs to ground? I think you have an open windings in the motor. Not a short or grounded compressor. (In fact, you compressor better be grounded.) Otherwise you would trip the breaker. What were the resistance readings across the compressor terminals? This is basic electrical troubleshooting.


    Quote Originally Posted by Royal241 View Post
    Here is what I found: at the compressor we have black yellow red terminal wires. the black goes through an external overload, there is also an internal overload. I followed the wires to the main electric panel. This is a 3 phase panel feeds are black red blue. What I did find was at the breaker the wires didn't correspond to right color: had red to black, white to blue, black to red. I rewired the breaker so I have from the main feed black to black, red to red, blue to yellow all the way to the compressor. I have to learn more about the phase thing (panel wise), but so far I believe that was what went wrong, wrong voltage to compressor winding, like I said, I have to look more into this for the future, any suggestions? I replaced compressor and it runs as was intended to, nice all around.

  10. #10
    Join Date
    Mar 2008
    Location
    North Queensland, Australia
    Posts
    1,051
    Post Likes
    Quote Originally Posted by carmon View Post
    it happens..... single phased maybe.... who knows......
    2 phase, not single phase. if there's only 1 phase to it nothing will happen. 2 phases will cook it.
    Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002

  11. #11
    Join Date
    Mar 2008
    Location
    North Queensland, Australia
    Posts
    1,051
    Post Likes
    Quote Originally Posted by Royal241 View Post
    2 months ago I installed a 1HP 3Ph 404a walk in cooler. I did a test run for 2 days, no problem. Unit was shut down, today construction of restaurant is over and inspector coming tomorrow (health inspector). Owner turned all the stuff on but the cooler didn't work. I found the compressor grounded, what did it? I shut it down (2 months ago) from a pump down switch inside the cooler that shuts down the solenoid and fans. In the mean time we had a bad storm around here, but owner said they didn't lose power. I will replace compressor in the morning, but I just don't want to believe that **** happens. So, any suggestions?
    If you just shut the system down by turning off the pump down switch in the cold room then left the site for 2 months what makes you think it stayed off for that period?

    I assume there were builders in the place for the duration who would have liked nothing better than a nice cold room to store their lunch and cold drinks in.

    If you're going to leave a room for a long period of time under the described conditions, do yourself a favour and pump the machine down from the receiver outlet valve, valve off the suction service valve at the compressor and disconnect power from the condensing unit and lock off or at least tag off the isolator.

    That way if you return to the site and find the tag / lock gone and or the valves open, you know that someone has been playing silly buggers and sorry, no warranty.



    Quote Originally Posted by Royal241 View Post
    Voltage is good all across, protector was opened and never reset itself, I bypassed it to see what happens, nothing happened, I was getting voltage all across 3 terminals but no amperage, that's what makes me scratch my balls, breaker didn't trip, all connections tight, no acid, I kicked (boot kicked) the compressor, checked for ground and now was no more. I checked resistance and I had none across 2 winding terminals (must've moved brains out of the comp with my kick). What happened here? What caused it to get grounded in off cycle? Any suggestions would be nice, would really jump start my brain, I ran out of ideas, Thanks and cheers guys.
    By protector do you mean an int69 thermistor protection unit? If so it won't reset till you take power off it. after that, if it doesn't reset and your compressor is cold, either it's stuffed or you've got a crook thermistor in the windings.

    no resistance across 2 winding terminals as in the ohm meter read 0? Or do you mean you had infinite resistance between the 2 terminals? (as in no circuit)

    And once more, as you weren't there for 2 months and only switched it off at the fan switch in the room, you have no way of knowing if it was off or not. Particularly when the afore mentioned storm came through and you only have yourself to blame for that.

    Hope that helps. Oh, and you may want to get some powder for that itch.
    Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002

  12. #12
    Join Date
    Mar 2008
    Location
    North Queensland, Australia
    Posts
    1,051
    Post Likes
    Quote Originally Posted by Royal241 View Post
    Here is what I found: at the compressor we have black yellow red terminal wires. the black goes through an external overload, there is also an internal overload. I followed the wires to the main electric panel. This is a 3 phase panel feeds are black red blue. What I did find was at the breaker the wires didn't correspond to right color: had red to black, white to blue, black to red. I rewired the breaker so I have from the main feed black to black, red to red, blue to yellow all the way to the compressor. I have to learn more about the phase thing (panel wise), but so far I believe that was what went wrong, wrong voltage to compressor winding, like I said, I have to look more into this for the future, any suggestions? I replaced compressor and it runs as was intended to, nice all around.
    Phase rotation doesn't matter unless it's a scroll compressor. You obviously have your proper 3 phases there or the new compressor wouldn't be running.

    Out of curiosity, when you found the old compressor not working, was it hot?

    And is it a scroll? What's its model number?
    Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002

  13. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Slatts View Post
    2 phase, not single phase. if there's only 1 phase to it nothing will happen. 2 phases will cook it.

    You are joking, right?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  14. #14
    Join Date
    Dec 2009
    Posts
    26
    Post Likes
    Thread Starter
    Was cold. I have never seen a compressor like that one, 3 ph with an external protector on one leg (same as in single phase ones). As I said, the protector never closed and I jumped it, well I got a grounded compressor, braker popped, then kicked compressor and there was no more ground to it, just one winding opened. Well, it's been one month now, the new compressor is doing just fine, got it under warranty, if cope and finds something wrong on my side, then I should hear from them...maybe. Thanks for suggestion, beer cooler for construction dudes, it might have happen. I didn't want to go back to the job site so that's why I shut it off the way I did, guess I learned something new by now...was cold out there that day...high roof, etc. Thank you guys for being thoughtful.

  15. #15
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by Royal241 View Post
    Was cold. I have never seen a compressor like that one, 3 ph with an external protector on one leg (same as in single phase ones). As I said, the protector never closed and I jumped it, well I got a grounded compressor, braker popped, then kicked compressor and there was no more ground to it, just one winding opened. Well, it's been one month now, the new compressor is doing just fine, got it under warranty, if cope and finds something wrong on my side, then I should hear from them...maybe. Thanks for suggestion, beer cooler for construction dudes, it might have happen. I didn't want to go back to the job site so that's why I shut it off the way I did, guess I learned something new by now...was cold out there that day...high roof, etc. Thank you guys for being thoughtful.
    So out of curiosity, did the new compressor have the same "overload" configuration as the dead one?

  16. #16
    Join Date
    Dec 2009
    Posts
    26
    Post Likes
    Thread Starter
    You are kidding me, I like that, Duhhh. Man that was funny, I'm licensed and now my ****. RST97C1E TA5. It came out of a RLH125M44E. I will get off my high horse and do what I do best without your answer. For one I will think I had a bad compressor and know that I did a proper install.

  17. #17
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    615
    Post Likes
    Royal:
    What was the kidding post in relation to?
    I don't think anyone is trying to grind your gears...the "you are joking statement by 2sac was directed at Slatts if that is what you are talking about.

  18. #18
    Join Date
    Mar 2008
    Location
    North Queensland, Australia
    Posts
    1,051
    Post Likes
    Quote Originally Posted by 2sac View Post
    You are joking, right?
    If you have only 1 phase hooked up to a 3 phase motor you'll have the same potential at all 3 terminals. nothing will happen till you connect another phase.

    3 phases it will run, 2 phases it will cook and hopefully trip its safety, 1 phase it will do nothing.
    Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002

  19. #19
    Join Date
    Dec 2009
    Posts
    26
    Post Likes
    Thread Starter
    No man, Ryan thinks I had a single phase and connected it to a 3 phase, don't you see about the configuration? Slatts is a kool dude

  20. #20
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Maybe the terminology is different between here and Australia. A single "leg" won't cause any harm. The second leg is the 208/230 "single phase" which will kill a 3 phase compressor.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •