    So I have been looking into buying a gas powered generator. It has come down to one or two things. Hoping to get some info here:

    AVR: Automatic Voltage Regulator
    TDH: Total Harmonic Distortion

    Will a generator having AVR technology give you low/low enough TDH to run sensitive electronics.

    It has come to my attention that a low TDH, 5% or lower is needed to run flat screens, laptops, etc safely. If a generator was to have a higher TDH could a quality surge protector such as Monsters filter this for electronics?

    My other concern is with my HVAC. I have a Carrier Infinity furnace w/ 2 stage coiling down stairs and a Performance series HP upstairs. I am concerned that if the power is not clean enough it will damage the circuit boards, ECM's, gas valve, etc. Or cause a problem with the ignition control. Does anyone with knowledge of this have an opinion?

    I had a guy call me the other day and said his gas furnace worked fine until he needed to use his Generac GP800E generator. I believe he said it will lite but not stay lit, could be wrong. I am guessing the generator is effecting the flame sensing.

    The only generator's I have found so far that claims it can safely run electonics are the Generac XP series which has True Power Technology and runs below 5% THD and and the Briggs & Straton Pro Series which states it's AVR can hold a 3%-6% THD.

    In my research I have found that all Generac's have an AVR. But not Briggs & Straton.

    In closing I am leaning towards the Generac XP10000E. I have left out Honda because they seem so freaking expensive for the same technology. If you can make the case for the Honda have at it and provide a M# that seems like it compares in technology.

    Thanks all

  2. #2
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    6,943
    Post Likes
    I wonder the same things even with a less sophisticated HVAC system. I've used our generator for PCs with a surge type protective strip but never an entertainment center or our new furnace using flame rectification. I was thinking, in a pinch in heating season, that I would just wire around the board and send 24 volts to the gas valve, 120 to the blower and start it manually and stop it with a separate stat. A royal pain, but it would provide some heat.

    I'm really hoping I never have to find out, but I might just do a test next time I start the generator and stabilize the gas.

    Also heard there maybe a filter of sorts to clean up the dirty juice from the generator???

  3. #3
    Join Date
    Dec 2010
    Location
    Vancouver, BC
    Posts
    25
    Post Likes
    The new inverter Gensets seems to produce very clean power. Have run several pieces of very sensitive electronics with Honda's EM5000iS. Also used the EU2000 for electronics. Both produce clean sine waves.

    Iv run the EM5000 with sensitives electronics and large inductive loads starting and you dont even notice it. That think purs no matter whats connected.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,244
    Post Likes
    The bottom line for Gen power is whether or not you are producing a true sinusoidal waveform. Many modern gen sets will do this.

    Consider the load spectrum on your normal power company service. It starts as a three phase rotating sinusoidal field at the power station. For residential, one of those phase legs is fed to a transformer, where the two ends of the secondary become your two ungrounded service conductors, with a secondary center tap that is grounded at the transformer and which becomes your service neutral, tied to an earth ground of some type at your service entrance.

    Everyone on the local area fed by that phase leg from your substation has a variety of loads. Many of these loads are both inductive AND non-linear. So, the power coming into your home often has transients and harmonic distortion, and voltage is not as steady as we would like to see. This is due to the increased use of non-linear devices like compact fluorescent lighting and the many motor loads that change the power factor of the grid. As this increases, utilities will have to take more steps to improve power factor for residential grids.

    Look at the waveform of a typical CFL bulb:

    Name:  CFL Lamp waveform.jpg
Views: 1698
Size:  17.1 KB

    So, if you are using a modern gen set, the chances are good that the power you are producing for use in your home is more than capable of meeting the quality that you are normally receiving from your utility.

    By the way, many power utilities have quietly allowed the line frequency to vary from the sacrosanct 60 Hz that was almost a laboratory standard. Apparently, the tightly controlled frequency costs money to maintain, and allowing it to vary slightly brings a cost saving to the power industry.

    So, a true sinusoidal output from a Gen means you are likely good to go for any residential load.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #5
    Join Date
    Aug 2006
    Posts
    3,055
    Post Likes
    Hondas have low oil shutdown, not sure if the other engines have this.
    I only have to make it work till I retire.

  6. #6
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,063
    Post Likes
    call your carrier dealer they have a line of standby generators that hook to the natural gas line or propane tank , carrier generators are rebadged generac
    Go Trump

  7. #7
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    538
    Post Likes
    Thread Starter
    Quote Originally Posted by Zoltrix View Post
    The new inverter Gensets seems to produce very clean power. Have run several pieces of very sensitive electronics with Honda's EM5000iS. Also used the EU2000 for electronics. Both produce clean sine waves.

    Iv run the EM5000 with sensitives electronics and large inductive loads starting and you dont even notice it. That think purs no matter whats connected.
    The EU series does not produce enough wattage. I am looking for at least 7-8K watts. Would prefer more. I really do not wan't to get two. Just one to power my whole panel and select loads by breakers. The EM5000s and EM5000is seem like very good generators. Nice that the is has the inverter. But they cost so much. I cant believe there technology and engines are just that much better. They are the only generator in the 5K watt range that I have seen with an inverter though. But it is not eneough wattage for me. At the cost of Hondas I would start to think about a whole house generator. But I will be moving so not a option.

  8. #8
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    538
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    So, if you are using a modern gen set, the chances are good that the power you are producing for use in your home is more than capable of meeting the quality that you are normally receiving from your utility.

    By the way, many power utilities have quietly allowed the line frequency to vary from the sacrosanct 60 Hz that was almost a laboratory standard. Apparently, the tightly controlled frequency costs money to maintain, and allowing it to vary slightly brings a cost saving to the power industry.

    So, a true sinusoidal output from a Gen means you are likely good to go for any residential load.
    Thanks timebuilder. It seems that I should be safe with any of the newer higher end units. I am thinking if it has an idle control and some type of AVR I will be good. My brother inlaw has picked up a Generac XG8000E. I think I may try his out.

  9. #9
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    538
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    call your carrier dealer they have a line of standby generators that hook to the natural gas line or propane tank , carrier generators are rebadged generac
    Is there any benefit to this? I would be connecting the generator to my intire panel. The generator and panel will still have an earth ground.

  10. #10
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    538
    Post Likes
    Thread Starter
    Quote Originally Posted by madhat View Post
    Hondas have low oil shutdown, not sure if the other engines have this.
    Everyone I have looked at has this safety shutdown. Pretty sure any known brand has it.

  11. #11
    Join Date
    Jul 2002
    Location
    Chariton, Iowa
    Posts
    512
    Post Likes
    A couple thoughts, PCs aren't nearly as sensitive to bad power as many think, the first thing most non or passive power factor corrected switched mode power supplies do with the power is run it through a bridge rectifier and into a large filter capacitor, or in the case of 115/230 switchable PC power supplies, when set to 115 it is 2 capacitors in series, 1 is charged by the positive peak of the wave, the other is charged by the negative peak. Active PFC is a different animal. Some active PFC controller ICs are just picky and won't even run on a modified sine inverter.

    What is more important for SMPS is a proper wave peak voltage as that determines what the capacitors get charged up to, see what timebuilder posted. A non PFC unit only draws current when the instantaneous input voltage is higher than the DC rail voltage, hence why the current is drawn in pulses. The peak voltage of a pure sine is 1.414x the RMS so the SMPS expects the DC rail to be at 160-170 or 320-340v

    These current pulses on a cheap generator with too high of a winding resistance cause the sine wave to become flat topped, thus reducing the peak voltage.

    Also flame rectification microamp sensing furnaces require that the neutral and ground be bonded. My POS True Blue 90 runs just fine on my cheap Chinese 2 stroke ~1kw generator (the same one that is sold all over the place under various names and labeled from ~800-1200 watts).

  12. #12
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    6,943
    Post Likes
    Quote Originally Posted by danielthechskid View Post
    A couple thoughts, PCs aren't nearly as sensitive to bad power as many think, the first thing most non or passive power factor corrected switched mode power supplies do with the power is run it through a bridge rectifier and into a large filter capacitor, or in the case of 115/230 switchable PC power supplies, when set to 115 it is 2 capacitors in series, 1 is charged by the positive peak of the wave, the other is charged by the negative peak. Active PFC is a different animal. Some active PFC controller ICs are just picky and won't even run on a modified sine inverter.

    What is more important for SMPS is a proper wave peak voltage as that determines what the capacitors get charged up to, see what timebuilder posted. A non PFC unit only draws current when the instantaneous input voltage is higher than the DC rail voltage, hence why the current is drawn in pulses. The peak voltage of a pure sine is 1.414x the RMS so the SMPS expects the DC rail to be at 160-170 or 320-340v

    These current pulses on a cheap generator with too high of a winding resistance cause the sine wave to become flat topped, thus reducing the peak voltage.

    Also flame rectification microamp sensing furnaces require that the neutral and ground be bonded. My POS True Blue 90 runs just fine on my cheap Chinese 2 stroke ~1kw generator (the same one that is sold all over the place under various names and labeled from ~800-1200 watts).
    Good to know, Thx.

  13. #13
    Join Date
    Nov 2013
    Posts
    3
    Post Likes
    Great info in this thread! I also want to know if it is safe to power my Carrier Infinity furnace with a portable generator through a manual transfer switch. I have asked Generac and Carrier customer support sites and only got CYA liability responses. I am torn between a Generac XG10000E and the XP10000E. They both have AVR. I like the XP because it has an electronic governor, and "True Power Technology" which they say brings THD < 5%. Cons: it costs about $1,000 more and has full GFCI on all outlets. This causes the GFCI to trip because the generator ground is bonded to neutral in the generator. Generac says the dealer can break the bond and keep the unit under warranty. However, in this thread, "danielthechskid" says: "flame rectification microamp sensing furnaces require that the neutral and ground be bonded". I guess my question is whether a generator like the XG with >5% THD, and a mechanical governor would keep the Carrier Infinity electronic controls and that very expensive software controlled blower motor happy?

    Thanks for any insight!