Results 1 to 9 of 9
  1. #1
    Join Date
    Apr 2009
    Location
    massachusetts
    Posts
    95
    Post Likes

    Leak testing with nitrogen

    I always thought nitrogen stayed the same pressure in a system even if ambient temps change from one day to another.Do you guys see this to be true?

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    69,738
    Post Likes
    Nitrogen is subject to pressure changes at varying temperatures, just not as much as refrigerants and other gases are.
    ...seek, and ye shall find;..
    So always seek the Truth, not just what you want to believe to be true…
    Ecclesiastes 10:2 NIV


  3. #3
    Join Date
    Apr 2009
    Location
    massachusetts
    Posts
    95
    Post Likes
    Thread Starter
    Got it,If I put in 300psi and return in a day or two and temps are ten degrees of each other,what do you think 5psi give or take?

  4. #4
    Join Date
    Dec 2011
    Location
    New Zealand
    Posts
    2,733
    Post Likes

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    http://hvac-talk.com/vbb/showthread.php?t=846662

    Here's a good thread on the topic.

    If I remember right, there's also a calculator that will allow you to compute what your target pressure should be, given known conditions.

  6. #6
    Join Date
    Mar 2007
    Posts
    3,629
    Post Likes
    Quote Originally Posted by burto View Post
    Got it,If I put in 300psi and return in a day or two and temps are ten degrees of each other,what do you think 5psi give or take?
    I think at this point, you know as much about the system as you would if you had done nothing at all. Do a real leak test, or at the very least pull a vacuum and see if it holds. Don't be lazy.

    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  7. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    5,987
    Post Likes
    300psi? A little overkill maybe?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  8. #8
    Join Date
    Jul 2012
    Location
    Athens, GA.
    Posts
    152
    Post Likes
    Here is a snippet about ideal gas law that will answer you question.

    Name:  2012-11-03 22.50.44.jpg
Views: 251
Size:  167.5 KB

  9. #9
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,886
    Post Likes
    I recently used this formula for a system that required me to document a standing 24 hour pressure test at 600 psi. I pumped it up and ended up with 604 psig on my digital Testo. Also took temp reading. Wasn't able to come back next day, ended up being 5 days and pressure was at 608 psig. I don't remember the temp change, it wasn't much, but using the forumla, it showed that 608 was right where I needed to be.

    Jim Bergman wrote an excellent article for RSES on how to calculate the pressure change for standing pressure tests. It is in the RSES Journal Archives.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.