Results 1 to 9 of 9
  1. #1
    Join Date
    Apr 2009
    Location
    massachusetts
    Posts
    44

    Leak testing with nitrogen

    I always thought nitrogen stayed the same pressure in a system even if ambient temps change from one day to another.Do you guys see this to be true?

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,437
    Nitrogen is subject to pressure changes at varying temperatures, just not as much as refrigerants and other gases are.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  3. #3
    Join Date
    Apr 2009
    Location
    massachusetts
    Posts
    44
    Got it,If I put in 300psi and return in a day or two and temps are ten degrees of each other,what do you think 5psi give or take?

  4. #4
    Join Date
    Dec 2011
    Location
    New Zealand
    Posts
    1,290

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,944
    http://hvac-talk.com/vbb/showthread.php?t=846662

    Here's a good thread on the topic.

    If I remember right, there's also a calculator that will allow you to compute what your target pressure should be, given known conditions.

  6. #6
    Join Date
    Mar 2007
    Location
    Home of the newly wed and the nearly dead
    Posts
    2,941
    Quote Originally Posted by burto View Post
    Got it,If I put in 300psi and return in a day or two and temps are ten degrees of each other,what do you think 5psi give or take?
    I think at this point, you know as much about the system as you would if you had done nothing at all. Do a real leak test, or at the very least pull a vacuum and see if it holds. Don't be lazy.

    Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.

    "It's called the american dream because you have to be asleep to believe it" -George Carlin

    "A nation of sheep begets a government of wolves" -Edward R. Murrow

    "I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney

    Buy american made goods & support locally owned businesses!

  7. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,743
    300psi? A little overkill maybe?
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  8. #8
    Join Date
    Jul 2012
    Location
    Athens, GA.
    Posts
    143
    Here is a snippet about ideal gas law that will answer you question.

    Name:  2012-11-03 22.50.44.jpg
Views: 165
Size:  167.5 KB

  9. #9
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    6,340
    I recently used this formula for a system that required me to document a standing 24 hour pressure test at 600 psi. I pumped it up and ended up with 604 psig on my digital Testo. Also took temp reading. Wasn't able to come back next day, ended up being 5 days and pressure was at 608 psig. I don't remember the temp change, it wasn't much, but using the forumla, it showed that 608 was right where I needed to be.

    Jim Bergman wrote an excellent article for RSES on how to calculate the pressure change for standing pressure tests. It is in the RSES Journal Archives.