    gas lines

    Never use anything less than 1/2" for gas lines. Used to be in the old BOCA plumbing code.

    If any crap blew into that valve, it will clog the pilot filter. Try this:

    First, pull that 3/8ths gas line and feed it to the nearest dumpster. Run a 3/4" line to within 10 ft. of the Fp, then you can reduce to 1/2" for the final run. If it still craps out, replace the valve. Also, replace the pilot orifice spud if still pooping out.

    The pressure at the heater 4 feet from the reg. is going to be a lot higher than at the Fp 40 feet away! Keep in mind that spec. for 5.0 wci is under full load--furnace and Fp.

    Manometers can read pressure but not flow.


    Ask those geniuses with the air hose if they were going to install a water separator so they don't add more water into the lines. If this is CSST, you'll never get all the water, pipe dope, and crap out of it. Just another case for replacement.

    Check the vent limit cap on that Max. 325-5. Just remove it and see if it makes a difference. This isn't vented to the outside is it? Any chance they overpressurized the Fp before someone thought to install the MP reg.?
    HTH

  2. #15
    Join Date
    Jan 2005
    Posts
    448
    Reviewed original post and have to agree with Colin & Hearthman, 3/8" line could definately be a problem!

  3. #16
    Join Date
    May 2005
    Location
    Madison, WI
    Posts
    1,078
    uhh... why would the inlet pressure be the same at the fireplace as the boiler? The lines are different lenghts and sizes. With loads on them that creates different pressure drops. As I already said the inlet on the FP prob is dropping to 0 when you turn the bioler on.

    I would be questions the skills of those so called "Pros" you hired.

    BTW I have only been in the fireplace business for 3 years and I it sounds like I know more about gas lines than those guys.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event