Results 1 to 13 of 15
    Nov 2012
    Richmond Va
    New heat pump installed.
    Last month I had a complete new system installed with all new duct work. The new system was working awesome (even temp throught home) untill about 3 to 4 days ago. The issue is half the house can be 71 and the other is 69. The installer added a small return for the side that now is 1 to 2 dregrees colder. So I did some looking and what I found was that the new return is almost closed shut. Looks like flex duct was use at the return.
    I know a quite a bit about airflow! I had a few hotrods. I know for a fact that to get air to make a 90 degree turn you have to have a gradual bend.
    What should the total air flow for a 3 ton system be? Is there a min/max system pressure that can be messured?
    Suggestions to what to ask the installer to check??
    To me, a 2° difference is great. You'll have different loads at times such as afternoon sun or lights and people. He can play around forever trying to balance airflow but since this load varies, it will never be perfect.
    Jun 2006
    Richmond, VA
    It's hard to say without seeing the duct and what you have for balance problems. Adding a return helps the available supply static pressure and therefore affects flow into the room.....but it does it for the whole supply duct system so the hot side will get more air too. 2 degrees isn't that much due to the fact 1 thermostat centrally located with duct going to a bunch of rooms with different heating and cooling loads.....
    If the duct is sealed well, and depending on the equipment, fan on low for recirculation MIGHT get you perfect.
    I wish I had a $1.00 for every response I deleted.....
    "Decidedly Superior in a twisted pathetic way".....
    Northeast Ohio
    I agree that 2 degrees is minimal considering variable heat gain/losses that are prevalent in most structures. It may be possible for the contactor to balance the system using dampers keeping in mind that the conditions will change heating to cooling season. I might possibly try running the system blower in a continuous low speed circulation mode to see if that helps balance out the temperature.
    DEM
    Jun 2001
    +4, 2 degrees is great
    Athens, Ohio
    for 2 degrees. Same for running the fan. I will guess that the weather has changed recently and you now have more heat gain (or loss) in certain areas of the house at different times of the day.
    Nov 2000
    Eastern PA
    Quote Originally Posted by JJoe View Post
    Nominal amount of air for a 3 ton system should be 1,200 CFM.
    The shorter the distance where the conditioned air must travel to "return" to the system, the less temperature difference there will be. Flex ducting must be as straight and pulled as taut as is reasonable to be most effective.
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Nov 2012
    Richmond Va
    Guy's thanks for your insight! Since I have a Perstige IAQ 2.0 thermostat I have already thought about and ordered a remote Stat as the main one is not located in a central location. That should resolve my little issue! Its hard not to worry when you spend $$$$$. Again I thank you for your time. Have a wonderful day.
    Set the fan to circ, and see if that doesn't help.
    Nov 2000
    Eastern PA
    Good idea, especially if your system has an ECM blower that runs at 50% volume in fan mode when no heat or cooling is being called for.
    Also, shut off the supply regester closest to the thermostat.
    Rochester NY
    ...and maybe bump the setting a degree or two.
    Nov 2012
    Richmond Va
Size:  144.7 KB It just looks like to me that it can't flow much if any air. It's no more than 1 inch from the top of the sheet metal.
    Jun 2001
    Looks like the straight piece of sheet metal should have been a "hard 90". Hard to say for sure w/o seeing the job.