Hi guys, should secondary pumps flow be equal or greater than the primary flow, i mean, when choosing pumps for chilled water system, should i install secondary pumps that are greater in flow capacity than the primary pumps or both should be equal?
Many thanks,
-
11-02-2012, 03:09 PM #2
Pump should be selected based on the flow necessary for the circuit.
Climate Control Solutions for your Home or Office
Serving Northeast Philadelphia and Surrounding Areas
-
11-02-2012, 03:16 PM #3
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
This thread should be in one of the "Chillers" section. Ask a moderator to move it. Try clicking on the "!" in the lower left corner of your post. I'm thinking the secondary pump(s) should be sized based on the load (and lift?), and the primary pump(s) should be sized based on their respective chiller(s). But I'm not certain. Maybe I'm wrong about moving this thread. Is it a residential application? I was not aware primary/secondary loops were used there.
-
11-02-2012, 03:21 PM #4
Regular Guest
- Join Date
- Apr 2010
- Posts
- 7
-
11-03-2012, 08:36 AM #5
Moved to Tech to Tech.
-
11-03-2012, 05:02 PM #6
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
11-03-2012, 05:32 PM #7
Primary pump= flow of the device doing the work.
Secondary pump= sized for the load.
Think of it this way, there can be numerous primary and/or secondary pumps..... This should clarify the thought process...
I have a building with two primary pumps (one for each chiller) and two secondary pumps (building split into two phases) but only one water system.
GTIf a day goes by and you have learned nothing, I hope you got a lot of sleep.
-
11-03-2012, 07:14 PM #8
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 297
This may help
-
11-04-2012, 04:46 AM #9
Regular Guest
- Join Date
- Apr 2010
- Posts
- 7
-
11-04-2012, 02:40 PM #10
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 297
You are welcome. It was posted by someone else.
-
11-05-2012, 01:34 PM #11
Regular Guest
- Join Date
- Jun 2010
- Location
- Miami
- Posts
- 249
You would always want primary flow to be larger than secondary flow. You can violate that for short periods but doing so for any degree of time will cause lots of problems with humidity and such.
-
11-05-2012, 06:09 PM #12
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
-