    carrier burner lights sometimes

    Carrier 48dje064ca package unit with 3 burners. Gas pressures ok, pilot tubbing cleaned but, one burner (first stage) will only ignite when I hold hand over exhaust vent. Other burners run, same type of vendor motor on all 3 burners Anyone have an idea why by holding back exhaust it will allow burner to fire?

  2. #2
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Is the wind deflector missing?

  3. #3
    Join Date
    Jul 2007
    Posts
    76
    Post Likes
    Thread Starter
    Yes. They were all missing ang found replacements

  4. #4
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Maybe a wind problem. I have made some wind deflectors out of sheetmetal.

  5. #5
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    You have the post count. You should apply for pro membership. You will get a lot more answers.

  6. #6
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    It could have a restricted orfice on the burner that doesn't light. You said this unit has a pilot tube, does the ignitor light the pilot at the burner that doesn't fire? The Carrier RTU's I usually work on have an ignitor with cross overs to light all the burners.

  7. #7
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Looketh for spider webeths in your orfices

  8. #8
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Quote Originally Posted by mikeacman View Post
    Looketh for spider webeths in your orfices
    Check this. Very common on the carrier units.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Wow, that's an old Carrier to have a pilot tube. I haven't had a customer that is still running that era in over two years.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Also spider webs in your pilot tube

  11. #11
    Join Date
    Jul 2007
    Posts
    76
    Post Likes
    Thread Starter
    The pilot tube had been removed and cleaned. You can see pilot flame along bottom of tubing, but peeters out when it hits top tubing(u bend) and doesn't seem to hit sensor to open main gas, until vent is plugged.

  12. #12
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    703
    Post Likes
    check the heat excahnger for a crack in that tube.

  13. #13
    Join Date
    Jul 2007
    Posts
    76
    Post Likes
    Thread Starter
    Heat exchanger changed in August, baffles included

  14. #14
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    Quote Originally Posted by iceage View Post
    The pilot tube had been removed and cleaned. You can see pilot flame along bottom of tubing, but peeters out when it hits top tubing(u bend) and doesn't seem to hit sensor to open main gas, until vent is plugged.
    Have you tried to increase the pilot gas pressure and did you check the orifice on the pilot tube?

  15. #15
    Join Date
    May 2012
    Posts
    27
    Post Likes
    might not be getting enought gas pressure coming out of valve

  16. #16
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    I got a bunch of these I work on, they SUCK!!! What I've found is the newer crossover tubes didn't get drilled out right from the factory... If its an old one that is in decent shape should be good there, don't change it unless you like drilling out the last straight section of crossover tube... It takes about an hour to do.

    But the first thing is check the pilot orifice as has been said.. Always use a orifice drill kit with the right size bit.

    Couple of other things to check are the baffles in the heat exchanger. Are they in there or rusted out? Air leakage around the draft motor will cause some issues too.

    You can also run the pilot pressure in and out to see if it makes a difference.. I still haven't made a tee yet to test the pilot pressure.

    I also can't say I've never made the pilot orifice a size bigger.

  17. #17
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Oops, missed where you said you cleaned the orifice and the baffles were replaced...

    Did the crossover tube get changed with the heat X? Or the gas valve?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •