Results 14 to 17 of 17
Thread: carrier burner lights sometimes
-
11-06-2012, 05:05 PM #14
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 347
-
11-11-2012, 05:28 PM #15
Professional Member
- Join Date
- May 2012
- Posts
- 21
might not be getting enought gas pressure coming out of valve
-
11-11-2012, 06:41 PM #16
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
I got a bunch of these I work on, they SUCK!!! What I've found is the newer crossover tubes didn't get drilled out right from the factory... If its an old one that is in decent shape should be good there, don't change it unless you like drilling out the last straight section of crossover tube... It takes about an hour to do.
But the first thing is check the pilot orifice as has been said.. Always use a orifice drill kit with the right size bit.
Couple of other things to check are the baffles in the heat exchanger. Are they in there or rusted out? Air leakage around the draft motor will cause some issues too.
You can also run the pilot pressure in and out to see if it makes a difference.. I still haven't made a tee yet to test the pilot pressure.
I also can't say I've never made the pilot orifice a size bigger.
-
11-11-2012, 06:45 PM #17
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
Oops, missed where you said you cleaned the orifice and the baffles were replaced...
Did the crossover tube get changed with the heat X? Or the gas valve?



Reply With Quote