carrier burner lights sometimes
Carrier 48dje064ca package unit with 3 burners. Gas pressures ok, pilot tubbing cleaned but, one burner (first stage) will only ignite when I hold hand over exhaust vent. Other burners run, same type of vendor motor on all 3 burners Anyone have an idea why by holding back exhaust it will allow burner to fire?
-
11-02-2012, 01:08 PM #2
Is the wind deflector missing?
-
11-02-2012, 01:16 PM #3
Regular Guest
- Join Date
- Jul 2007
- Posts
- 65
Yes. They were all missing ang found replacements
-
11-02-2012, 01:20 PM #4
Maybe a wind problem. I have made some wind deflectors out of sheetmetal.
-
11-02-2012, 01:21 PM #5
You have the post count. You should apply for pro membership. You will get a lot more answers.
-
11-02-2012, 08:40 PM #6
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 347
It could have a restricted orfice on the burner that doesn't light. You said this unit has a pilot tube, does the ignitor light the pilot at the burner that doesn't fire? The Carrier RTU's I usually work on have an ignitor with cross overs to light all the burners.
-
11-03-2012, 08:23 AM #7
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
Looketh for spider webeths in your orfices
mikeacman
-
11-03-2012, 10:51 AM #8
-
11-03-2012, 11:39 AM #9
Wow, that's an old Carrier to have a pilot tube. I haven't had a customer that is still running that era in over two years.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
11-03-2012, 12:17 PM #10
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
Also spider webs in your pilot tube
mikeacman
-
11-05-2012, 12:45 PM #11
Regular Guest
- Join Date
- Jul 2007
- Posts
- 65
The pilot tube had been removed and cleaned. You can see pilot flame along bottom of tubing, but peeters out when it hits top tubing(u bend) and doesn't seem to hit sensor to open main gas, until vent is plugged.
-
11-05-2012, 12:51 PM #12
Professional Member
- Join Date
- Jun 2012
- Location
- Northeast
- Posts
- 115
check the heat excahnger for a crack in that tube.
-
11-06-2012, 09:25 AM #13
Regular Guest
- Join Date
- Jul 2007
- Posts
- 65
Heat exchanger changed in August, baffles included


Reply With Quote