Results 1 to 13 of 17
    carrier burner lights sometimes
    Carrier 48dje064ca package unit with 3 burners. Gas pressures ok, pilot tubbing cleaned but, one burner (first stage) will only ignite when I hold hand over exhaust vent. Other burners run, same type of vendor motor on all 3 burners Anyone have an idea why by holding back exhaust it will allow burner to fire?
    Nov 2007
    Mississippi
    Is the wind deflector missing?
    Yes. They were all missing ang found replacements
    Nov 2007
    Mississippi
    Maybe a wind problem. I have made some wind deflectors out of sheetmetal.
    Nov 2007
    Mississippi
    You have the post count. You should apply for pro membership. You will get a lot more answers.
    Sep 2006
    Ohio
    It could have a restricted orfice on the burner that doesn't light. You said this unit has a pilot tube, does the ignitor light the pilot at the burner that doesn't fire? The Carrier RTU's I usually work on have an ignitor with cross overs to light all the burners.
    May 2002
    Looketh for spider webeths in your orfices
    mikeacman
    Dec 2008
    Buffalo NY
    Quote Originally Posted by mikeacman View Post
    Check this. Very common on the carrier units.
    Join http://scopeny.org/ Shooter’s Committee on Political Education
    The world is full of sheep,try not to join the flock.
    Support the Skilled Trades, Don't DIY
    Southeastern Pa
    Wow, that's an old Carrier to have a pilot tube. I haven't had a customer that is still running that era in over two years.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    May 2002
    Also spider webs in your pilot tube
    mikeacman
    The pilot tube had been removed and cleaned. You can see pilot flame along bottom of tubing, but peeters out when it hits top tubing(u bend) and doesn't seem to hit sensor to open main gas, until vent is plugged.
    Jun 2012
    Northeast
    check the heat excahnger for a crack in that tube.
    Heat exchanger changed in August, baffles included
