Thread: Supermarket various leaks

  1. #1
    Join Date
    Jun 2008
    Posts
    120
    Post Likes

    Supermarket various leaks

    Hello, I started for a new company this year and they don't do a lot of supermarket work but they do the largest supermarket in the city. The racks are quite old here and I find small leaks sometimes during repairs by finding oil and then I fix the leak. I spend the most time at this place at the moment and I want to start getting these leaks found and fixed but I dont have enough time to do the work thats currently needed never mind leak searching. I want to know what tools and techniques you supermarket guys use to find leaks and lets just say money is not a issue for purchasing of tools. Your help is greatly appreciated, Thanks

  2. #2
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Flash light, electronic leak detector, ultrasonic leak detector, soap bubbles, mirror, and patience. Most leaks ain't to hard to find but some will require you to pull your truck on the roof and use every tool you have. A good vacume pump and micron gauge are a must as well. I start with mechanical connections and service valves, 90% of your leaks will be found there. Then onto the coils starting with tube sheet. Then onto the accumulators and receivers, the accumulators mounted upright will rust out on bottom and hide from you. Last is the lineset and brazed connections. Not every leak will show oil so don't assume if there's no oil there's no leak.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    OK.

    You say that the racks are "quite old" Let's be more specific... Are they 10 years old? 20? 40?


    Start with this. CLEAN THEM. Take a nice bucket of soapy water and a good degreaser and clean them up and keep 'em clean. It'll help with spotting the slow, oily weeper leaks.

    Now, fire up a GOOD electronic leak detector. I could go on a rant about which ones that I like and what I think of those that I don't, but we're looking for leaks, now, so get the one that you've got. I'll stick with my H-10PM. Walk the cases. Make a note of where you pick up leaks. You've got a lot of ground to cover, so don't try to stop and fix them all, just find 'em and note them and note from the detector's behavior if it was a big leak, a medium sized leak or a little leak.

    Now, you've got a list to work from. Sit down and organize it and create a plan of attack. Start with the largest leaks and work down from there. Be patient, you aren't going to fix them all after lunch on a Friday.

    Repeat this process with the mechanical room, the condensers and any auxiliary coils like heat reclaim.

    Now, start over. Sometimes, larger leaks tend to mask smaller leaks and it takes time to let the excess refrigerant dissipate.


    Now, you've got a tight store with nice, clean racks. KEEP IT THAT WAY.

    Do monthly leak checks, clean up the oil that you spill or that results from leaks.



  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by goodguyu View Post
    I dont have enough time to do the work thats currently needed never mind leak searching.
    I want to take a minute to specifically address this statement.

    If you don't stop and take the time, MAKE the time to do what is needed and do it correctly the FIRST time, then you will NEVER have the time to do it correctly.

    Putting a half-a**ed repair on a piece of equipment just to run to another call to slap a band-aid on it to get to the next call....

    Then, what happens is the half-a**ed, band-aided repairs start to unravel and you wind up starting to run call-backs intermixed with normal break downs.

    Now, you've got even LESS time to do what needs done.

    So, what do you do? Make quicker repairs. Use lighter bandaids. Add MORE gas to buy yourself more time until they call back again when it leaked out.

    STOP THE MADNESS!


    Ok, I'm going to step off of my soap box, now and maybe have a beer. I think I need one....




  5. #5
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    Installing a systematic leak detection system will help and i guarantee you it will pay for its self. But like jp says you gotta fix the leaks.

    If the store is r22 and has a high concentration that a halide torch can help you pinpoint leaks too.

  6. #6
    Join Date
    Sep 2006
    Location
    Chicago
    Posts
    491
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    I want to take a minute to specifically address this statement.

    If you don't stop and take the time, MAKE the time to do what is needed and do it correctly the FIRST time, then you will NEVER have the time to do it correctly.

    Putting a half-a**ed repair on a piece of equipment just to run to another call to slap a band-aid on it to get to the next call....

    Then, what happens is the half-a**ed, band-aided repairs start to unravel and you wind up starting to run call-backs intermixed with normal break downs.

    Now, you've got even LESS time to do what needs done.

    So, what do you do? Make quicker repairs. Use lighter bandaids. Add MORE gas to buy yourself more time until they call back again when it leaked out.

    STOP THE MADNESS!


    Ok, I'm going to step off of my soap box, now and maybe have a beer. I think I need one....

    We do more grocery store work than anyone and what jp said is spot on. For us by the time you make it to the machine room, and set down your tools, the office is on the phone asking when you're going to be done. Those that throw bandaids on things get the most praise. The problem re-occures in a couple months and all is forgotten by the sloppy office. Never fails hot weather hits and we're bogged down with heat related issues and then all the call backs come back to bite you in the a**. Some hot days we have 40+ calls come in between a few service guys. Now you start putting bandaids on things because you want to get home one day. It's a team effort though and if half the guys won't cooperate and no one in the office has any experience or knowledge then you do the best you can. I run so many call backs from some guys it's embarrasing.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by steve wright View Post
    Installing a systematic leak detection system will help and i guarantee you it will pay for its self. But like jp says you gotta fix the leaks.

    If the store is r22 and has a high concentration that a halide torch can help you pinpoint leaks too.
    I'm somewhat skeptical of these systems.

    They're a great HELP in catching leaks early, but nothing but NOTHING is better than a skillful and determined technician on the ground with a good electronic detector.



  8. #8
    Join Date
    Jun 2008
    Posts
    120
    Post Likes
    Thread Starter
    The original store racks are about 35 years old from what i'm told and are 134a and 507. The other additional racks are about 20 years old and are also 507 134a. The problem with this place is the band aid repairs are everywhere and work like this has been done like this for years due to the lack of time or know how. I'm definetly not doing bandage repairs myself, I'm trying to figure out the best plan of attack to get things gradually sorted out and in shape. I'm sorting out a time frame for a week of leak finding and repairs but I want to make sure I'am productive with my time since I've never went leak hunting in a supermarket before. When you say "walk the cases" do you simply mean putting the leak detector into the bunker air stream to see if it picks up on anything. The degreasing of the racks and clean up I can have done easily by sending a apprentice. Thanks for the help

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Walk the cases. Yep, just what you think. Put the detector in every case and see what happens.

    A week might be OK, but I wouldn't let myself get tied down to it.



  10. #10
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Tools I use for leak checking:
    H10-PM
    Tif ZX-1
    Bubbles
    nitrogen


    Turn on your leak detector and let it calibrate outside in fresh air.

    Walk into the store.

    If you get immediate leak detections as you walk in, shut off the air handlers, make up airs, & exhaust fans...stop air movement in the store.

    Leak check the sales floor cases by sticking the detector in the discharge air stream of the cases.
    If you have underground line penetrations, leak check the stub ups.
    If you have overhead lines, keep and eye out for stained ceiling tiles, it could possibly be oil.

    Leak check the walk-in boxes, inside of them and on top of them.

    Leak check the motor room.
    Shut down the racks while leak checking the motor room, and anything that moves air in there, like exhaust fans.

    leak check where the lines penetrate the motor room.
    Over head lines, stick the detector through the wall.
    Underground lines, stick the detector down the penetration.

    If you have overhead lines, usually there is some kind of "cat walk" that will allow you to walk around in the ceiling. If so, leak check up there.
    If the over head lines are inaccessible without a lift. Then you will need to leave them alone until you can prove there is a leak & its nowhere else.
    Then you need a lift, or pressurize inaccessible lines with nitrogen...but again, only if there is a proven leak & it's not detected anywhere else.

    Leak check the condenser, again, with the racks off so you can shut the fans off to stop air movement.

    Leak check air handlers cooling coils, reheat coils with the blower motors off.

    Then once you start finding leaks, depending on where they are. There are tricks to pinpoint, isolate, repair them. But as you find them, we can all address them at that time.

  11. #11
    Join Date
    Sep 2006
    Location
    Chicago
    Posts
    491
    Post Likes
    Hussmann smg service case coils leak a lot. We replace them all the time. Also don't be alarmed if your leak detector goes off in a hot water heat reclaim tank. The insulation will make it go off. Do a standing pressure test if you think it's leaking. I use the exact setup phase loss does. The tif zx is the most sensitive leak detector on the market. I also use the H-10 with it.

  12. #12
    Join Date
    Jun 2008
    Posts
    120
    Post Likes
    Thread Starter
    Thanks for all the excellent help guys Ill be sure to use some of these strategy's.

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by dangpgt97 View Post
    Hussmann smg service case coils leak a lot. We replace them all the time.


    Right at the spot where they hung the top coil by those little aluminum straps



  14. #14
    Join Date
    Sep 2011
    Location
    Plainfield IL
    Posts
    101
    Post Likes
    I agree with dangpgt... I have had great luck with the battery operated tif ZX1 and also love my H10 plug in ...hate the plug in though. As far as using your h10 I was taught to put it on the small leak size then dial it in till you barely hear the tick. If you swipe it in a cooler and it goes off it means there is a leak almost guaranteed.

  15. #15
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    I want to take a minute to specifically address this statement.

    If you don't stop and take the time, MAKE the time to do what is needed and do it correctly the FIRST time, then you will NEVER have the time to do it correctly.

    Putting a half-a**ed repair on a piece of equipment just to run to another call to slap a band-aid on it to get to the next call....

    Then, what happens is the half-a**ed, band-aided repairs start to unravel and you wind up starting to run call-backs intermixed with normal break downs.

    Now, you've got even LESS time to do what needs done.

    So, what do you do? Make quicker repairs. Use lighter bandaids. Add MORE gas to buy yourself more time until they call back again when it leaked out.

    STOP THE MADNESS!


    Ok, I'm going to step off of my soap box, now and maybe have a beer. I think I need one....

    Heck No JP! Get back on that soap box. Sure wish you could convince my ex-boss of that way of thinking. Read my sig line and that is what I am talking about. Why do all these companies want you to put a band aid on just about every call you run. Do half of what you said you were going to do on the maintenance. Need 2-3 call backs on almost every installation.

    I guess I just don't get it. I must be real dumb or something, thinking that the smartest way to get the work really done is to get it, do it right, make sure it is right, then leave the site.

    I really like the above explanation on how to really care for a rack.

    Thanks!
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  16. #16
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    All of this is great advice.

    Couple things to add. When we leak check, we try to divide things up so it does not seem so overwhelming. ie....start with low temp rack. Start with one line set at a time. If your low temp racks have hot gas defrost, put the section your are checking into defrost while your are sniffing with your leak detector, as the increased pressures can help your find smaller leaks.

    Patience and persistence is key.

  17. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by joemach View Post
    Heck No JP! Get back on that soap box. Sure wish you could convince my ex-boss of that way of thinking. Read my sig line and that is what I am talking about. Why do all these companies want you to put a band aid on just about every call you run. Do half of what you said you were going to do on the maintenance. Need 2-3 call backs on almost every installation.

    I guess I just don't get it. I must be real dumb or something, thinking that the smartest way to get the work really done is to get it, do it right, make sure it is right, then leave the site.

    I really like the above explanation on how to really care for a rack.

    Thanks!
    First day, first JOB, I saw a sign with a very similar sentence hanging over the door leading from the back room of a store onto the sales floor.

    "If you don't have time to do it right, when will you find time to do it over?"



  18. #18
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    First day, first JOB, I saw a sign with a very similar sentence hanging over the door leading from the back room of a store onto the sales floor.

    "If you don't have time to do it right, when will you find time to do it over?"
    ABSOLUTELY !

    Sure wish I could get into rack work. Only been a a few. Seems like they really wanted it done right. Just not much of it around here out in the sticks.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  19. #19
    Join Date
    Jul 2010
    Posts
    15
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    First day, first JOB, I saw a sign with a very similar sentence hanging over the door leading from the back room of a store onto the sales floor.

    "If you don't have time to do it right, when will you find time to do it over?"
    first thing I thought of when I read your first post in this thread
    http://www.goodreads.com/author/quot...41.John_Wooden
    fifth one down
    (the rest ain't bad neither !! )

  20. #20
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post


    Right at the spot where they hung the top coil by those little aluminum straps


    X2
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •