Results 1 to 13 of 17
    Nov 2008
    Northern California, foothills.
    Ruud heat pump outdoor coil error code, "coil sensor fail"
    Ruud heat pump outdoor coil.
    Cools just fine.
    Switch over to heating and
    the outdoor unit throws an error code,
    something like "coil sensor fail", (or failure or similar).
    Model number is UPNE-036JAZ
    The unit had been heating fine. Indoor unit, air-handler,
    was swapped out with a Bryant. Basic Honeywell tstat.
    Pro4000. Switched to heat pump. Advanced setup
    menu item 1 switched to heat pump as well.
    Am I going nuts or was I wrong to expect to see
    control voltage at Y terminal at the air-handler
    and outside unit upon a call for heat?
    Five minute delay was taken into account.
    Had to leave before I could systematically troubleshoot.
    I don't even get to return tomorrow. Senior guy is going
    out to ensure customer is happy.
    I'm simply puzzled and have to know what the problem is.
    For starters, what does Ruud mean by a "coil sensor fail"?
    Thank you.
    Nov 2011
    It's demand defrost...sensor measuring coil temp is faulty. Or at least, the board thinks it is.
    Nov 2008
    Quote Originally Posted by Saturatedpsi View Post
    You're beautiful.
    (Thanks.)
    Virginia
    Quote Originally Posted by georgelass View Post
    Basic Honeywell tstat. Pro4000. Switched to heat pump. Advanced setup menu item 1 switched to heat pump as well.
    Am I going nuts or was I wrong to expect to see control voltage at Y terminal at the air-handler and outside unit upon a call for heat?
    No you are not nuts, you should have a "Y" signal when there is a call for heat with a heat pump.
    I know this job has been given to someone else now, but I was just curious if this issue of "NO HEAT" started when the thermostat was replaced?
    If so, the Pro TH4110D thermostat needs a field installed jumper between "W" and "Y" for the compressor to energize in heat mode.
    The advanced setup you mentioned above, is only for the reversing valve to be energized.
    Dec 2006
    new england
    Very good point Rundawg...
    Chaos equals cash$$$
    Nov 2008
    The no heat started when we replaced the air-handler. The old one had a leak.
    But the installer undid a bunch of things and he might not have noticed some
    things and there was talk between homeowner and installer about somebody
    previously monkey-rigging things to get it to work.
    I did not talk to the tech that visited the problem today, but he did
    say a two-stage heat thermostat would be necessary. He might have
    addressed the Ruud heat-pump unit's error code. Maybe a loose wire?
    No word on that.
    Hey, jumping W to Y at the tstat was the last thing I did before I left yesterday.
    I left my best gauges at that site, I think, or out in the parking lot, and now
    they are gone. That thought is starting my weekend out on a bad note.
    Thank you for the help everybody.
    Jul 2009
    South Carolina
    If its a new air handler with an X13 or ECM motor then its possible the "Y" from the t-stat is not hooked up to the indoor board which would make the blower motor only run at about 1/2 speed. That could cause the outdoor unit to cut out on high pressure.
    Gary
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    Dec 2014
    I've got the same problem, diagnostic on defrost board code coil sensor failure doesn't matter what t stat calling for.
    Sep 2009
    Marietta, GA
    Quote Originally Posted by MatthewLovelock View Post
    ohm out the coil sensor to see if its bad. Good luck
    Dec 2014
    117.8 ohm's ...
    Quote Originally Posted by mofotech View Post
    still not clear on how to use this site
    Feb 2013
    Cary NC
    I had to contact manufacturer to see the ohm value should be to the corresponding oat. Lennox thing....
    Madison In.
    Rheem has the b terminal too. R.v. energized in heat
    Dec 2014
    Well had someone else look at it and he determined that the sensor was reading too high which confirmed it. Seriously though what happened to the days when something was broke it didn't work period.