  1. #53
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    Maybe I am. Seems you're the only one that feels that way. Testing flame sensors is hvac101. You should have learned it in school. If not ask for a refund.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  2. #54
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    You're checking for microamps. If your meter doesn't have a microamp setting you are SOL
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  3. #55
    ok thank you now we getting some where micro amps ,i think my meter doesnt check for micro amps but like you hvac101 ,can i wrap the wire around the jaws and divide and get a micro amp reading

  4. #56
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    No. Microamps are checked in series with the sensor. You need the proper meter.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  5. #57
    oh yes you are right direct current right i would have 2 place the meter in series with the flame censor circuit and get the amp reading this way . so you telling me i need a special meter to do this i paid 200 for my meter it should do this function so what meter i need then.

  6. #58
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,205
    Quote Originally Posted by Joehvac25 View Post
    Makes sense, I've heard the glass story, ever hear that?
    No I don't believe so.
    Contractor locator map

    How many times must one fix something before it is fixed?

  7. #59
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,205
    Check uA reading.
    Contractor locator map

    How many times must one fix something before it is fixed?

  8. #60
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,205
    Merged threads. Please don't make duplicate threads bout the same problem, thank you.
    Contractor locator map

    How many times must one fix something before it is fixed?

  9. #61
    Join Date
    Jan 2002
    Location
    tip of the mitt
    Posts
    1,873
    possible ground issue.
    I have my own little world. But it's OK...they know me here.

  10. #62
    Join Date
    Jul 2010
    Location
    Eastern Kentucky
    Posts
    54
    I maybe wrong , but I do not think there is a industry standard for ratings in microamps a flame rod should be putting out. One unit maybe different from the other. If the manufacturer had some information on the required output from flame sensor then measure it and if out of range replace it.

  11. #63
    Join Date
    Dec 2007
    Posts
    3,853
    some modules have that info imprinted on their sticker.

  12. #64

    ground for flame censor

    should this ground be located on the burners connected all the way back to the groud going to the main power coming in the unit . let me know

  13. #65
    Join Date
    Dec 2007
    Posts
    3,853
    why do you keep creating additional threads for the same topic?