Thread: DIRECT IGNITION PROBLEM SHOULD BE SIMPLE!

  1. #61
    Join Date
    Jan 2002
    Location
    tip of the mitt
    Posts
    2,005
    Post Likes
    possible ground issue.
    I have my own little world. But it's OK...they know me here.

  2. #62
    Join Date
    Jul 2010
    Location
    Eastern Kentucky
    Posts
    55
    Post Likes
    I maybe wrong , but I do not think there is a industry standard for ratings in microamps a flame rod should be putting out. One unit maybe different from the other. If the manufacturer had some information on the required output from flame sensor then measure it and if out of range replace it.

  3. #63
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    some modules have that info imprinted on their sticker.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  4. #64
    Join Date
    Jul 2012
    Location
    Atlanta ga
    Posts
    291
    Post Likes
    Thread Starter

    ground for flame censor

    should this ground be located on the burners connected all the way back to the groud going to the main power coming in the unit . let me know

  5. #65
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    why do you keep creating additional threads for the same topic?

    keep this in the original thread so it has some continuity in process.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  6. #66
    Join Date
    Jul 2012
    Location
    Atlanta ga
    Posts
    291
    Post Likes
    Thread Starter
    sorry bout that

  7. #67
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Merged threads.

  8. #68
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Youngwiseman View Post
    should this ground be located on the burners connected all the way back to the groud going to the main power coming in the unit . let me know
    You have enough posts to apply for Pro membership now.

    I'll be happy to answer your technical questions in the Pro forums.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #69
    Join Date
    Jul 2012
    Location
    Atlanta ga
    Posts
    291
    Post Likes
    Thread Starter

    i need help

    Quote Originally Posted by timebuilder View Post
    You have enough posts to apply for Pro membership now.

    I'll be happy to answer your technical questions in the Pro forums.
    i will apply a.s.ap. but i really need help. i have replace the flame censor and i still have the same results ,the burners lights up but after 3 to 5 seconds it goes right out ,right when the hsi deenergizes the burners shut off,ok, i would greatly appreciate some one explaining these grounds for me ,i have a ground wire coming from my disconnect box , and i have a ground wire and screw on the primary side of the transformer i hooked them up,same result ,the ground on the secondary side is good ,gas valve good ,continuity in flame censor wire is good ,so what is going on ,can my ifc be bad from this simple problem , ifc cant read the signal from the flame censor to keep my gas valve open wow ,cant be please let me know something

  10. #70
    Join Date
    Feb 2012
    Location
    Toronto Canada
    Posts
    1,090
    Post Likes
    So did you "Purge" the line yet?

    Keep throwin parts at it sooner or later the air will be out of the line

  11. #71
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    If the burner lights, I doubt there is air in the lines. Does the control board have a blinking light on it? If so, is it a steady blinking, or does it blink a few times, then pause, and then blink some more? You usually need to look through a little clear plastic circle in the door panel to see it, because once you remove the door it will stop blinking. Let us know what the blinking light is doing.

  12. #72
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Guessing you still don't have a manometer or a meter to check uA. You don't want to apply for professional membership. If you are unable to ask your employer or another tech for help, maybe you are just looking for DIY which is not allowed here. Good luck
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  13. #73
    Join Date
    Jul 2010
    Location
    Eastern Kentucky
    Posts
    55
    Post Likes
    The burners are the ground, The IFC sends AC signal to flame rod. The flame passes over the flame Rod, The current will actually flow through the flame from the Flame sensor to the burner ( which is the ground) because the flame can actually conduct electricity but it rectifys its signal and converts the AC to DC current. The IFC senses this DC signal through its ground connection to furnace. Make sure the ground connection to IFC is in good shape. This whole situation may not even be your problem you may be barking up the wrong tree. Is Your Pressure switchs dropping out because your flue pipe is stopped up? what kinda of furnace is this 90%?

  14. #74
    Join Date
    Jul 2012
    Location
    Atlanta ga
    Posts
    291
    Post Likes
    Thread Starter

    smile

    Quote Originally Posted by 2sac View Post
    Guessing you still don't have a manometer or a meter to check uA. You don't want to apply for professional membership. If you are unable to ask your employer or another tech for help, maybe you are just looking for DIY which is not allowed here. Good luck
    lol @you and your negativity ,gotta love it, i can do any thing myself sir because i am certified in hvac sir,so actually im certified to do everything you do ,are you jealous hope cause im the one confused here with this simple problem and i have applied for pro membership sir . thank you,nice talking to you but anyway....

  15. #75
    Join Date
    Jul 2012
    Location
    Atlanta ga
    Posts
    291
    Post Likes
    Thread Starter
    Ok ,no air in gas line ,no need to purge,gas flow and pressure is good , gas company made sure of this,now as for the blinks ,i have 1 blink , which means ignition failure, probable causes are gas flow gas pressure,flame sensor ,or ifc allare good ,now im a electrician also so tomarrow im going to start from the disconnect switch and hook up all grounds securely ,now i see no wire coming from the burners that seem like its connected to ground so should i tie a ground wire to the primary ground or secondary ground i have both, help.

  16. #76
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Youngwiseman View Post
    lol @you and your negativity ,gotta love it, i can do any thing myself sir because i am certified in hvac sir,so actually im certified to do everything you do ,are you jealous hope cause im the one confused here with this simple problem and i have applied for pro membership sir . thank you,nice talking to you but anyway....
    Let's make some things clear.

    First, from your user name, you just MIGHT have an attitude problem. When I read the post above, I am CERTAIN of it. If you were as good as that post I just quoted suggests, you would be giving info here, and not asking for it.

    So, pick up a large Mrs. Smith's Humble Pie, and dig in.

    Second, the help you are seeking is not provided in open forums. Whomever you work for has the responsibility to answer your questions, and once you get Pro membership, you can ask them in the Pro forums.

    Third, work on your written communication. Unless English is your second language, or you have a brain tumor, you have no excuse to not post in a clear, logical manner. Being successful in this business REQUIRES the ability to express thoughts clearly in writing and speaking.

    Fourth. comprehend the writing of others. Once you were told to get Pro membership, that's that. It is the only way that you will not be identified as a potential DIY poster. If you are a working pro, all you have to do is produce the required info, and bang, you can ask anything you want, and guys here will fall over themselves trying to help you get better at this.

    So, let's review.


    Stow the attitude, write and read clearly, get Pro membership, and then ask.

    Simple. No offense intended.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  17. #77
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Have these folks been without heat since November 1?

  18. #78
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Youngwiseman View Post
    Ok ,no air in gas line ,no need to purge,gas flow and pressure is good , gas company made sure of this,now as for the blinks ,i have 1 blink , which means ignition failure, probable causes are gas flow gas pressure,flame sensor ,or ifc allare good ,now im a electrician also so tomarrow im going to start from the disconnect switch and hook up all grounds securely ,now i see no wire coming from the burners that seem like its connected to ground so should i tie a ground wire to the primary ground or secondary ground i have both, help.
    Some furnaces will need a very good ground, and unless you have an unusual problem from the panel or disconnect, that is not your issue. Unless you have a ground issue from the module or board on the furnace, going to your burners, then that ground (bond, in reality) is not the issue, either.

    You need to measure rectification current, which is easy unless the HSI doubles as the flame sensor, as it can on some models.

    Your most likely path to the cause is the failure of the circuitry to see a consistent flame proving input.

    No step by step instruction in the open.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  19. #79
    Join Date
    Jul 2012
    Location
    Atlanta ga
    Posts
    291
    Post Likes
    Thread Starter
    Quote Originally Posted by hurtinhvac View Post
    Have these folks been without heat since November 1?
    yep

  20. #80
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Youngwiseman View Post
    ok...my meter huh ....ohm,amps,volts,? during the heating after burners lit ,i put my clamp on meter on it and read like 0.3 give or take 2 amps is this right
    Quote Originally Posted by Youngwiseman View Post
    should this ground be located on the burners connected all the way back to the groud going to the main power coming in the unit . let me know
    Quote Originally Posted by Youngwiseman View Post
    i would greatly appreciate some one explaining these grounds for me
    Quote Originally Posted by Youngwiseman View Post
    so actually im certified to do everything you do
    Quote Originally Posted by Youngwiseman View Post
    now im a electrician
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

+ Reply to Thread
Page 4 of 15 FirstFirst 123456789101114 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •