    DIRECT IGNITION PROBLEM SHOULD BE SIMPLE!

    Hello, I have a customer who's heat is not working. I approach the furnace and see what I have, I jumped the r to w and everything did as its suppose to do ,when my burners lit it stayed on for about 4 to 8 seconds and shut off now from my knowledge and experience I have had a furnace that did this once before and it was simply the flame sensor rod needed cleaning. I tried to run the system twice, both times main burner shut off so I disconnected the flame sensor rod cleaned it with sand paper and also if that didnt work I was going to test it by disconnectng the the wire from the terminal and placing one lead on terminal and one lead on flame rod wire from my knowledge any direct current above 2,0 is good and below 1.6 is a bad flame rod but after I clean the rod and install it back into the furnace the hot surface igniter lights but burner want light at all, I do have 24 volts coming from ifc,to valve all switches are closed roll out limit switches etc they should because no reason for them to open when there is no fire.

    From my knowledge I feel like its no gas pressure or no gas flow the gas valve has a coil ohm reading of 98.0 ohms I think thats about right because from another job I replaced a gas valve and the reading was 60 something and the new one read about 90 some thing or 100 ohms so gas valve I suspect is good. And the customer gas was just cut back on yesterday morning, and another thing that bothers me there is no shut off, drip tap, or union near this unit. So I feel the first 2 times the burners lit was old gas that was still in the line, first I need to see is the shut off open, I dont have a water manometer to check the gas pressure in and out the valve, any suggestions, I know the sequence of operation and all, I am a certified tech but nothing but 4 years experience still come across problen that I have to go back to my book for, I know I am in the ball park because to me heat cycle is very simple, worse case senario ifc is bad which I doubt. Input output is good or gas valve is not functioning correctly but I doubt also , and another thing the blink lights is one blink which mean ignition failure probable causes gas pressure no gas ,gas valve, flame sensor, and if this could be cause by a open limit or roll out or over temp stack let me know but I seriously doubt it because I think these open when burner is lit, let me know pros and service techs.
    Last edited by beenthere; 11-03-2012 at 09:46 AM. Reason: Got rid of all caps, added some punctuation

  2. #2
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    Was that all one sentence? And why do my ears hurt?

  3. #3
    Join Date
    Jan 2010
    Location
    new orleans
    Posts
    251
    Post Likes
    SO I'VE HEARD

  4. #4
    Join Date
    Jan 2012
    Location
    Tallahassee,Fl
    Posts
    144
    Post Likes
    Check the obvious first, if its LP check the tank maybe empty, if natural gas meter may be locked out due to no pay....

  5. #5
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Youngwiseman View Post
    I DISCONNECTED THE FLAME SENSOR ROD CLEANED IT WITH SAND PAPER
    I lost you after this, but you never clean a flame sensor with sandpaper, steel wool at the most, I usually just use a dollar bill.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    DONT POST IN CAPS!!!!!!!!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #7
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    Quote Originally Posted by Youngwiseman View Post
    ....I DONT HAVE A WATER MANOMETER TO CHECK THE GAS PRESSURE IN AND OUT THE VALVE, ANY SUGGESTIONS, .....
    One all caps run-on sentence and this jumped out at me. You should not be touching the appliance without this most basic service tool.

    Other than that please stop posting in all caps and add some punctuation.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  8. #8
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    "... I DONT HAVE A WATER MANOMETER TO CHECK THE GAS PRESSURE IN AND OUT THE VALVE, ANY SUGGESTIONS..."

    match!
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  9. #9
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    I DON'T KNOW WHAT WE'RE YELLING ABOUT!!!

    I love lamp

  10. #10
    Join Date
    Feb 2011
    Location
    Indianapolis, IN
    Posts
    34
    Post Likes

    Several "issues " and then some

    I would address the gas pressure and and train not having union, drip leg,or gas cock are code violations to start with...

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Got rid of the all caps.

  12. #12
    Join Date
    Sep 2012
    Location
    Ottawa, Canada
    Posts
    28
    Post Likes

    Thumbs up

    I've seen the bill trick when I was in training. Ya don't want to be rough on it. Good advice to new techs.

  13. #13
    Join Date
    Sep 2012
    Location
    Ottawa, Canada
    Posts
    28
    Post Likes
    I never heard it called a water manometer, regardless, you need more than a manometer to do this job, and done by a trained professional. You can cause a lot of problems and dangers if you don't know what your doing.

  14. #14
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Get a digital manometer, **** after 4 years you don't have a manometer that's crazy. That's what u nesd


    Sent from my iPhone using Tapatalk

  15. #15
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    It lit twice, then you cleaned the flame sensor, now it won't lite, what did you do?

    You don't need a manometer to tell if you have gas pressure to a unit, just to know if you have the correct pressure. Think about it.

    If the gas was just turned back on yesterday I would think the gas company would have bled the line, but maybe not if he ws green.

    You say you have 24v to valve, does it "click", can you feel it?

  16. #16
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    You don't need a manometer to test for pressure but with no experience I don't want to tell him how to check though it should be a no brainier.


    Sent from my iPhone using Tapatalk

  17. #17
    Join Date
    Jul 2010
    Location
    Eastern Kentucky
    Posts
    55
    Post Likes
    First of all what is up with all the insults everyone? writing in cap locks... Who cares? you don't have to read it if you don't want to and run on sentences? come on! be easy on youngwiseman I mean he is only seeking advice! don't shoot him down. hes been in the field 4 years, give him a break buttholes.

    Ok youngwiseman can you hear the gas valve click when 24 volts is applied to its coil. Do you hear gas hissing through the orifices on the burner manifold when the gas valve opens. Is your first orifice on manifold maybe clogged? If you suspect no gas than take your allen wrench and loosen the pressure tap on the inlet side of your gas valve and see if you have any, can you smell it?

    Is your pressure switchs making contact when inducer is running. maybe your flue pipe is partially stopped up (waspers nest) and dropping out the gas valve when the pressure switch is going back and forth clicking in and out

  18. #18
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by dgussler View Post
    First of all what is up with all the insults everyone? writing in cap locks... Who cares? you don't have to read it if you don't want to and run on sentences? come on! be easy on youngwiseman I mean he is only seeking advice! don't shoot him down. hes been in the field 4 years, give him a break buttholes.

    Ok youngwiseman can you hear the gas valve click when 24 volts is applied to its coil. Do you hear gas hissing through the orifices on the burner manifold when the gas valve opens. Is your first orifice on manifold maybe clogged? If you suspect no gas than take your allen wrench and loosen the pressure tap on the inlet side of your gas valve and see if you have any, can you smell it?

    Is your pressure switchs making contact when inducer is running. maybe your flue pipe is partially stopped up (waspers nest) and dropping out the gas valve when the pressure switch is going back and forth clicking in and out
    First, we don't do ANY step by step in the open forums.

    Second, it does matter how he communicates, because style and substance are intertwined. If he can communicate clearly and succinctly, in an easy to read style, he will be much farther ahead in getting the info he needs. I stopped after about ten words, because I'm here to help, and not beat myself up trying to conform to an unconventional individual.

    If this guy is a tech, he needs to get his post count up to 15 and apply for Pro membership, and learn how to interact on the forum, so he can really benefit from the experience of this online community.

    Once he has Pro membership, he can ask technical questions in the Pro forums, and he will get lots of help.

    Fair enough? 'nuff said.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  19. #19
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by timebuilder View Post
    First, we don't do ANY step by step in the open forums.

    Second, it does matter how he communicates, because style and substance are intertwined. If he can communicate clearly and succinctly, in an easy to read style, he will be much farther ahead in getting the info he needs. I stopped after about ten words, because I'm here to help, and not beat myself up trying to conform to an unconventional individual.

    If this guy is a tech, he needs to get his post count up to 15 and apply for Pro membership, and learn how to interact on the forum, so he can really benefit from the experience of this online community.

    Once he has Pro membership, he can ask technical questions in the Pro forums, and he will get lots of help.

    Fair enough? 'nuff said.
    Well said, sometimes being tough makes the point sink farther.
    We don't know this person is a tech, these are questions he should ask his lead tech, though it is very easy according to the title.


    Sent from my iPhone using Tapatalk

  20. #20
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by pacnw View Post
    "... I DONT HAVE A WATER MANOMETER TO CHECK THE GAS PRESSURE IN AND OUT THE VALVE, ANY SUGGESTIONS..."

    match!
    GET ONE!!!
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

+ Reply to Thread
Page 1 of 15 1234567811 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •