    Maybe I am. Seems you're the only one that feels that way. Testing flame sensors is hvac101. You should have learned it in school. If not ask for a refund.
    Officially, Down for the count
    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them
  2. #54
    Oct 2011
    Chicagoland Area
    You're checking for microamps. If your meter doesn't have a microamp setting you are SOL
  3. #55
    Jul 2012
    Atlanta ga
    ok thank you now we getting some where micro amps ,i think my meter doesnt check for micro amps but like you hvac101 ,can i wrap the wire around the jaws and divide and get a micro amp reading
  4. #56
    Oct 2011
    Chicagoland Area
    No. Microamps are checked in series with the sensor. You need the proper meter.
  5. #57
    Jul 2012
    Atlanta ga
    oh yes you are right direct current right i would have 2 place the meter in series with the flame censor circuit and get the amp reading this way . so you telling me i need a special meter to do this i paid 200 for my meter it should do this function so what meter i need then.
  6. #58
    Quote Originally Posted by Joehvac25 View Post
    Makes sense, I've heard the glass story, ever hear that?
    No I don't believe so.
  7. #59
    Check uA reading.
  8. #60
    Merged threads. Please don't make duplicate threads bout the same problem, thank you.
  9. #61
    Jan 2002
    tip of the mitt
    possible ground issue.
    I have my own little world. But it's OK...they know me here.
  10. #62
    Jul 2010
    Eastern Kentucky
    I maybe wrong , but I do not think there is a industry standard for ratings in microamps a flame rod should be putting out. One unit maybe different from the other. If the manufacturer had some information on the required output from flame sensor then measure it and if out of range replace it.
  11. #63
    some modules have that info imprinted on their sticker.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ
  12. #64
    Jul 2012
    Atlanta ga
    ground for flame censor
    should this ground be located on the burners connected all the way back to the groud going to the main power coming in the unit . let me know