11-05-2012, 12:18 AM #53
Maybe I am. Seems you're the only one that feels that way. Testing flame sensors is hvac101. You should have learned it in school. If not ask for a refund.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-05-2012, 12:19 AM #54
You're checking for microamps. If your meter doesn't have a microamp setting you are SOL
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-05-2012, 12:28 AM #55
Regular Guest
- Join Date
- Jul 2012
- Posts
- 26
ok thank you now we getting some where micro amps ,i think my meter doesnt check for micro amps but like you hvac101 ,can i wrap the wire around the jaws and divide and get a micro amp reading
-
11-05-2012, 12:37 AM #56
No. Microamps are checked in series with the sensor. You need the proper meter.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-05-2012, 12:56 AM #57
Regular Guest
- Join Date
- Jul 2012
- Posts
- 26
oh yes you are right direct current right i would have 2 place the meter in series with the flame censor circuit and get the amp reading this way . so you telling me i need a special meter to do this i paid 200 for my meter it should do this function so what meter i need then.
-
11-05-2012, 05:17 AM #58
-
11-05-2012, 05:18 AM #59
Check uA reading.
-
11-05-2012, 05:23 AM #60
Merged threads. Please don't make duplicate threads bout the same problem, thank you.
-
11-05-2012, 06:58 AM #61
Professional Member
- Join Date
- Jan 2002
- Location
- tip of the mitt
- Posts
- 1,873
possible ground issue.
I have my own little world. But it's OK...they know me here.
-
11-05-2012, 07:12 PM #62
I maybe wrong , but I do not think there is a industry standard for ratings in microamps a flame rod should be putting out. One unit maybe different from the other. If the manufacturer had some information on the required output from flame sensor then measure it and if out of range replace it.
-
11-05-2012, 08:31 PM #63
some modules have that info imprinted on their sticker.
If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
11-06-2012, 11:05 AM #64
Regular Guest
- Join Date
- Jul 2012
- Posts
- 26
ground for flame censor
should this ground be located on the burners connected all the way back to the groud going to the main power coming in the unit . let me know
-
11-06-2012, 11:49 AM #65
why do you keep creating additional threads for the same topic?
keep this in the original thread so it has some continuity in process.If Guns Kill People, Do Pencils Misspell Words?