Fuse keeps blowing
My dad has a heat pump, when the heat is turned on the 3 amp fuse on the 24V red wire off the transformer is blown, a/c is fine. The transformer was replaced, the blower contactor reads 10 ohms across the coil, the backup heat contactor reads 15 ohms. Both work when contactor is pushed in.
Someone told me that one would check all the low voltage wires to see if they are shorted. Does that mean one would disconnect the wire at both ends (at the thermostat being one end) and then check it to ground, hoping to read OL? Since it's the heat not working, either the white or red wire would be shorted, correct?
Could it also be a motor problem?
I'm only a few months deep in this trade and I'm curious.
-
11-01-2012, 07:28 PM #2
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,257
it's being caused by a short circuit; now it is in your best interest to ask a co-worker or an instructor to give you guidance on the proper procedure to determine where that short is.
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
11-01-2012, 09:22 PM #3
I will give this fine piece of advice. Fuses do not go bad.
You have a direction follow the road stillyout find the trouble
-
11-01-2012, 10:30 PM #4
Professional Member
- Join Date
- Dec 2007
- Posts
- 605
-
11-02-2012, 01:14 PM #5
Is reversing valve energized in heat mode? What brand condenser does your dad have?
-
11-02-2012, 03:29 PM #6
Regular Guest
- Join Date
- Nov 2011
- Location
- USA
- Posts
- 197
You need to determine when the fuse blows: on a call for heat or second stage heat, during defrost, or just when the stat is set to "heat". If it's a Rheem product, could be the reversing valve circuit, since they energize in heat. You appear to have eliminated the aux heat control. Likely not the red wire or the fuse would blow in either mode. Check continuity on the "white" wire to common for low resistance. Based on the info you've provided it's the best bet for now.
-
11-03-2012, 02:07 AM #7
Might want to check the stat wire for continuity se if there is a short in the stat wire
-
11-03-2012, 07:53 AM #8
As a new tech, you should apply for pro membership so we can help you in the pro forums. Most technical information is not discussed out here in the open.
-
11-03-2012, 09:55 AM #9
Filing out your profile also helps us know who we are talking to.
-
11-03-2012, 01:39 PM #10
Regular Guest
- Join Date
- Dec 2011
- Location
- Mid-Atlantic
- Posts
- 7
Update: Someone came to help figure it out and he said it's probably thermostat trouble. We had a new thermostat put in by our local power company for free, which enables them to turn off our power for a short time if needed.
Do you think it could actually be a faulty thermostat? All the wires seem to be hooked up correctly.
Also for pro membership I think I need 15 posts correct?
-
11-03-2012, 01:52 PM #11
Professional Member
- Join Date
- Mar 2008
- Location
- NC
- Posts
- 1,338
Yes. When you'll find guys a lot more giving with advice in the non-public forums.
-
11-03-2012, 02:03 PM #12
-
11-03-2012, 07:34 PM #13[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17